Paralleling Battery Banks [RE-wrenches]
Ray Walters
walters at taosnet.com
Mon Jan 1 11:16:30 PST 2007
<x-flowed>
I noticed this in many "code" systems. Some controllers like the RV-50
from Blue Sky can actually be damaged if the batteries are disconnected
before the array current is removed. I believe they've fixed this issue
now. I've also noticed that if the inverter load is close to array
output, that the inverter can continue to run array direct. Its funny to
pull the main battery disconnect, and still have everything on. Some day
maybe we'll have an automated disconnect system, that will disconnect
charging sources first and then the batteries. Until then, we can label
away, but my customers don't seem to actually read all those labels we
stick on everything.
I'm working on an electric vehicle with 4 parallel strings of batteries.
I'm adding all copper interconnect resistances up to balance the bank (I
had to add 5 ft of #4 to one string for instance) The problem is that I
don't know where to put the fuses. A fuse at each battery positive would
protect the sometimes long runs under the vehicle, but the other 3
strings could back feed a potentially dangerous short without blowing
their fuses. So, do I put fuses on both ends of each cable, or just live
with the problem, as we do with most solar systems, where the main
battery cables are unprotected all the way into the DC load center.
Personally I would like to see batteries with integral fuses to protect
any short, even the classic "dropping a wrench across the terminals"
move. My kids' Barbie Jeep had sealed batteries with an ATC fuse that
plugged right into the top of battery.
We go crazy protecting systems from sometimes very improbable dangers,
while blindly ignoring the most dangerous source of fault current that
I'm sure all of us dealing with batteries have experienced personally.
Anyone smell something burning?
Ray Walters
William Miller wrote:
>
> Hugh:
>
> This is a very significant point you have raised. In the past I might
> have been a bit cavalier about opening battery breakers, but no more!
> I have drafted a warning sign that will remain in memory in my label
> printer.
>
> I always find something illuminating in your posts. Thank you.
>
> William Miller
>
>
> At 12:02 AM 12/31/2006, you wrote:
>
>> Take care that pulling a fuse will not leave the charging sources
>> connected to the inverter and controls without any battery. I would
>> use a separate fuse(s) for any charging sources, so that this is not
>> possible. A wind or hydro turbine that shares a fuse with the
>> inverter can be a source of dangerously high voltage if the fuse is
>> pulled. Charge controllers may or may not be able to deal with the
>> turbine output in the absence of batteries. I am not sure about PV
>> but I would imagine that the same problem would arise to a lesser
>> extent (lower open circuit voltage).
>>
>> I guess if you put a separate inverter fuse on each battery string,
>> then you need multiple fuses for the charging sources as well. Or
>> else place a conspicuous sign indicating the dangers of pulling out
>> all the battery fuses.
>> --
>> Hugh
>>
>> Scoraig Wind Electric
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list