Disconnects on Fronius [RE-wrenches]
Matt Thompson
matt at greenlotusconstruction.com
Fri Oct 20 09:28:43 PDT 2006
<x-flowed>
Hello,
In small systems without a fuse combiner box, I install an MC connection
on each positive DC leg inside the Fronius wiring box.
This is especially a good idea if getting to an MC conn on the roof is
difficult. When servicing the IG one has to push the MC plugs through
the knockout one at a time.
To me this solution seems to be a safe alternative to an external DCD.
Matt Thompson
Mark Frye wrote:
> I tend to agree much more with Dan on this issue. Note also that the
> brand with the X also uses an integrated "DC Disconnect".
>
> Once you have a fused combiner box, you essentially have an external
> disconnect.
>
> In a small system with just a few strings I don't have a fused
> disconnect and do have to get to the MC connector which are also "no
> load" disconnecting means. I always build with plenty of space between
> the array and the roof deck and home run connectors are always easy to
> get at.
>
> An electrician is a person who knows the hazards associated with working
> on electrical systems and knows how to protect themselves from those
> hazards. PV systems have their own particular hazards which can be
> addressed with specific protective actions.
>
> Just like any other aspect of electrical work, you shouldn't work on PV
> it if you don't know it. I think we should be focusing on disseminating
> appropriate safety measures for working on PV rather than putting a
> bunch of bells and whistles on methods that already have the basic
> protective elements available to the qualified individual.
>
> Berkeley Solar Electric Systems
>
>
> William Miller wrote:
>
>> Dan:
>>
>> I have to say I think you and Fronius are way off-base on this issue.
>> You
>> are encouraging installers to install systems unsafely just to save
>> themselves a few dollars. I presume this is to give Fronius some kind
>> of
>> market advantage.
>>
>> Here's an analogy for you: I could not install a roof-top air
>> conditioning
>> unit and have the disconnect for it at ground level. The disconnect has
>> to
>> be within line of sight of the unit. Human nature being what it is,
>> someone is going to remove a Fronius inverter and fail to get a ladder
>> and
>> climb up on the roof just to disconnect the DC feeder to the inverter.
>>
>> If Fronius had remained silent on the issue, that would be one thing,
>> but
>> actively encouraging installers to disregard common safety practices is,
>> in
>> my professional opinion, unconscionable.
>>
>> As I said, I like your product and I like your people. I disagree
>> strongly, for safety reasons alone, on this one issue.
>>
>>
>> Sincereley,
>>
>> William Miller
>>
>>
>>
>>
>>
>> At 12:16 PM 10/19/2006, Fortson Dan wrote:
>>
>>
>>> Hi William,
>>>
>>> I hope you are recovered from the SP-2006 event. I have read your
>>> comment
>>> on wrenches & will respond there as well. My stand on the Fronius
>>> disconnect & code compliance is somewhat more measured than Fronius
>>> techs
>>> in the past as I believe it's ultimately up to the inspector. I
>>> understand
>>> Mr. Wiles refuses to commit on the matter. The live wire issue is real &
>>>
>>> not trivial though. In fact, in the training I just gave at SP2006, I
>>> emphasized to those in the class, who would likely be the ones
>>> disconnecting a unit from the wall, that it is neither safe nor
>>> advisable
>>> to do so while the wires are hot. I generally recommend pulling string
>>> fuses or disconnecting one connector in each string, then checking with
>>> a
>>> volt meter or on the Fronius display that DC voltage is, in fact, zero.
>>> This method ensures that there will not be live wires unattended for
>>> children to play with, etc.
>>>
>>> Your solution of using an external DC disconnect ensures safety but many
>>>
>>> installers do not feel the trade-off is worth the investment. That's a
>>> personal decision which must be made by the installer.
>>>
>>> Hope to see you next year at the show,
>>>
>>> Dan Fortson
>>>
>>> Applications Engineer
>>>
>>> Fronius USA
>>>
>>> (810) 220-4414
>>>
>> __________________________________________________________________
>> William Miller
>> Miller Power and Communications
>> Voice :805-438-5600 Fax: 805-438-4607
>> email: wrmiller at mpandc.com
>> http://mpandc.com
>> License No. C-10-773985
>> _____________________________________________________________
>> Check out our latest project at
>> http://mpandc.com/case_studies/pv_school/pv_school.html
>> --
>> [Non-text portions of this message have been removed]
>>
>>
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list