"Point of Connection" To Tap, or Not to Tap" [RE-wrenches]
William Miller
wrmiller at charter.net
Fri Sep 15 08:56:15 PDT 2006
<x-flowed>
Bruce:
Are you installing a dedicated fused disconnect (which is exactly what the
section requires)?
When you want to install on the load side, the usual hitch comes with this
wording: "(2) The sum of the ampere ratings of overcurrent devices in
circuits supplying power to a busbar or conductor shall not exceed the
rating of the busbar or conductor." We would assume that in most cases the
ampacity of the conductor or busbar matches the ampacity of the service
OCP, therefore you have no reserve ampacity, unless this is a residential
installation, in which case you get 20%. If you violate the section (2)
above, you must connect to the supply side. Yes, it is scary, but it is
what the code requires.
To win a "pissing match" with the AHJ is a consideration of the
personalities involved. In many cases, if the inspector recognizes the
authority of an industry expert, a print out of an e-mail or article by
Bill Brooks or John Wiles may hold some weight in the argument. I have
also convinced inspectors in small municipalities by initiating a three way
dialog with the main county inspector who was in agreement with my
interpretation. There are in some areas professional organizations of
building inspectors. If you know a member that has an open mind and can be
convinced of your point of view, they could also exert some subtle
influence on your recalcitrant building official.
Good luck and let us know how this works out.
William Miller
At 09:52 PM 9/14/2006, you wrote:
>Hi all. Has anyone run into Article 690.64 being interpreted as
>prohibiting taps to the load side of the main service breaker? One
>particular municipality is saying that, even with a fused AC disconnect,
>taps are not allowed because of Item B (1) which says "Each source
>interconnection shall be made at a dedicated circuit breaker or fusible
>disconnecting means."
>
>The only issue that occurs to me is the protection of the section of
>wire between the tap and the fuse in the AC disconnect. Would it seem
>reasonable to size that section of wire equivalent to the service
>conductors?
>
>Has anybody else run into this? How have you handled it?
>
>The municipality in question suggests tapping on the supply side of the
>main breaker, but that seems much less safe. The current on the wire
>between the fused AC disconnect and the tap then only be limited by the
>overcurrent protection on the utility transformer, no?
>
>Thanks for you help.
>
>Bruce
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list