mondo off-grid inverters [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Sat Sep 9 05:10:08 PDT 2006
Chris
You have several of us interested, besides 36 kW 10
inverter 3 phase, can you give us some more specs? Is
it stand alone?
Can it be grid tied?
Does it use a special Hub or special inverter?
Can I use this technology for a 6 inverter three phase
system? (20 kW)
Thanks Darryl
--- Christopher Freitas --- OutBack Power
<cfreitas at outbackpower.com> wrote:
>
> Marco -
>
> There are some large stand-alone inverters out there
> - but the
> performance is usually surprisingly poor from a
> efficiency standpoint.
> Often the idle power consumption is in the 10% of
> the full power rating
> (so 3000 watts for a 30KW unit) and they often weigh
> thousands of pounds
> - real fun to move... Most of them also are not
> "hybrid" meaning they
> will not charge the battery either.
>
> We are fielding our first 36 KW three phase
> inverter/charger in the next
> few weeks and have many single and split phase 30 to
> 36 kW off-grid
> systems in the field now - some for several years
> already.
>
> Keep in mind that for 36 kW you only need TEN
> OutBack VFX3648 inverters
> - not the "dozens" you mentioned. Our idle power
> draw will be as low as
> 65 W DC for a 36 kW unit depending on the AC output
> configuration.
> Since we can turn on the additional slave inverters
> with increased load
> the efficiency is very good across the entire power
> range. All of the
> parts can be carried by one person and even
> installed solo.
>
> From my experience and research - all of the large
> military or
> commercial inverter you find will have a price that
> will be very high,
> less features and the lead time and service response
> unacceptable for
> most off-grid applications. Most also will require
> high DC battery
> voltages which introduces lots of design issues and
> safety concerns.
>
> I would be very interested in hearing other people's
> experience.
>
> Christopher
>
>
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas @ outbackpower.com
> www.outbackpower.com
> Arlington WA USA
> Tel 360 435 6030
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list