Keith -
The recommendation for the 2/0 AWG cable was based on using the FX3038
with a 175 amp DC disconnect breaker. If you are using a smaller
breaker than you can use a smaller cable naturally.
When the manual was written we were not confident on the time-delay of
the 100 amp breakers for starting larger motors. Since that time we
have been able to source a 125 amp version which is better. We are
using this with the PS1 system and the VFX3648 with 1/0 AWG cables and
it has been fine.
The issue with cable heating is not that significant - especially on the
shorter cable runs we have on our DC systems.