Hi Matt and All,


On 5/20/06 12:04 PM, "Matt Lafferty" <mlafferty at universalenergies.com>
wrote:

> 
> I see a couple of things "missing" from the descriptions in this thread for
> a conclusive determination of the true cause for the discrepancies...
> 
> 1) Hours of operation.  In many cases, even though it is generally
> "prohibited", the PV systems will have a number of hours or days
> "head-start" on the PV Generation Meters.

Our customer-owned utility-grade PV production KWH meters go into service
when the inverters do. The (separate) Utility-owned net meters usually take
awhile to get installed by the meter tech, though.

> 
> 2) Most revenue grade kWH meters account for power factor losses to some
> degree.  What this means is that a site with a low power factor actually
> "uses" more energy to do the same "work" as far as the meter is concerned.
> This is a double-bite for our purposes...

Thr KWH meters are on the inverter output, backfeeding a breaker in the
house system. Why should the meter be affected by the power factor of the
house loads or site (except, perhaps, for battery backup systems)?
{This is probably where I should simply say "Awww shucks" and "Golly gee"
and "I didn't know that... Wow!"} :)

> 
> 3) Most revenue grade kWH meters are very accurate in the "forward"
> direction (+/- .5%), but wildly vary in their accuracy when running
> "backward". This aspect is huge on a number of fronts and there isn't room
> to describe the plethera of scenarios here. You may be wondering "why would
> my PV meter run backward?"... Simple.  At nite, the inverter uses some AC
> power... A very small amount based on the Manus, but some nonetheless.  It
> is impossible to tell here what that effect has on the "dial readings".  The
> Inverter displays do not count this.

If inverter energy consumption at night is significant it seems to me that
the (inverter) meter should account for it. Or, at least have a "net total
production" reading.
> 
> 4) If you have a 120V Inverter, you need a 120V meter to properly meter it.
> Running the noodle through one leg of a 240V meter will not provide accurate
> results.  Period.

The meters we use are "120/240-V" For 120-V operation the hot leg is run in
series through all 4 jaws, the small latch on the back of the meter is
opened and connected to neutral. However, I don't know if the accuracy of
the meter is guaranteed in the 120V configuration. I'll check on this....
> 
> 5) Electro-mechanical vs. "calculated".  This is another spot where the
> differences get wild. Your PV Meter is most likely EM.  Inverter
> displays/meters are calculated.

This makes sense, but shouldn't account for 15 to 20% differences, should
it?

> Here are the high-points of my testing and research over the years:


Thanks for the input, Matt. I can see that, like many things that we do, the
answer isn't as simple as we would like it to be. I'll compare outputs
between the meters on a few grid-tied systems that have been running for at
least a year and post the results to the List.

-Kelly
Kelly Keilwitz, P.E.
Whidbey Sun & Wind, LLC
Renewable Energy Systems
NABCEP Certified PV Installer
987 Wanamaker Rd, 
Coupeville, WA 98239
PH & FAX 360-678-7131
sunwind at whidbeysunwind.com


The rest of what Matt said:

> 
> After eliminating #1 & #4 above, the largest discrepancy factor is a
> combination of #2 & #5. Once you've isolated and quantified them, multiply
> the Inverter meter reading by the average Power Factor.  You will be amazed
> how closely the result comes to matching the PV Meter reading.
> 
> How to go about doing it:
> 
> In order to track this, you'll have to get your hands on a recording
> analyzer that does power factor measurements.  (I.E. Fluke 43 or similar...
> ~$2K) If you don't have one, and most of us don't, it is possible to request
> a "power quality" or "meter accuracy" test from your utility company.
> 
> Generally they all do this at no charge.  You will have to tell them
> specifically what aspects you want results for and the interval that
> measurements are taken... Try to talk directly to the Power Quality Tech and
> let him/her know what you are trying to do.  They are generally pretty laid
> back and quite helpful if you aren't pushy or "blaming the big bad utility".
> They will let you know what they can measure/record at what intervals and
> for how long.  Generally speaking, the more channels you want measured
> reduces the length of time and increases the interval period for your test.
> After you get a decent relationship going, be sure to try to get the "data"
> as well as the standard "report".  Ask for it in a CSV or spreadsheet
> format.  This may or may not be possible due to "policy".  Generally
> speaking, you will get a lot more bees with honey, so be sure to have jelly
> donuts on hand.  Your attitude will play a large part in determining how all
> this goes. If you know you can't be civil with them, send somebody who can!
> (Hint: "Awww shucks" and "Golly gee" and "I didn't know that... Wow!
> Thanks!" will get you a long ways toward your goal... These guys are
> "tech-heads" by nature and they can talk way over your head in most cases...
> Way over mine, anyway. The "Awww shucks" thing plays nicely in getting the
> conversation onto a "plain English" level.)
> 
> Some utilities have power quality recorders available to Electrical
> Contractors on a loaner basis for use in their service territories.  Check
> into this option.

> 
> Matt Lafferty 
> Universal Energies Institute
> mlafferty at universalenergies.com
> (415) 252-0343 Phone
> (916) 914-2247 Fax
>  



 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
See the hottest games before your friends! Sign up with Ubisoft, 
and you'll get access to exclusive game news, contests, promotions, 
community forums, and more. It's easy, free, and secure.
http://click.topica.com/caaePuxbz8Qcsbz9JC9f/ Ubisoft
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-wrenches mailing list