I am working with small commercial group that runs various manufacturing
equipment in a small building.
The aging service is a 3 phase, 240V delta, with a 208V leg opposite the
neutral (I am not sure if it is called a "stinger leg" if it isn't
277V.) The service entrance conductors include 1 - 500 MCM grounded, 2 -
500 ungrounded, and 1 - 1/0 ungrounded (for the "stinger leg".) I have
not yet determined what type wire they are.
My understanding is that the stinger leg wire in the service drop is
also "undersized".
The service entrance conductors pass through a CT can and terminate in a
3 phase, 240V, 400A fused disconnect. The fuses are 2 - 400A, and a 300A
on the stinger leg (the 300A fuse is much newer than the other two.) I
have not yet tested or determined what loads are connected to the
stinger leg, what the demands actually are or why it was recently
replaced.
The utility has inspected this equipment and said they were not
interested in upgrading the service drop or requiring an improvement of
the service equipment.
One question I have is who owns the service entrance conductors? My
understanding is that the they belong to the premise and in this case
the stinger leg with the 300A fuse should be upgraded by the owner,
regardless of what the utility does with the drop. Or else, they should
replace the 300A fuse with a 150A.
However, since there is no capacity in the fused disconnect to back feed
a 30kW PV system, I will be connecting on the line side, in the CT can.
In this case the existing 1/0 is capable of handling the back feed
current.
I guess I need to really find out what kind of current is running in the
stinger leg.
If the 300A fuse is needed to serve the loads, I am thinking I will
upgrade the service entrance stinger leg conductor and do a line side
tap in the CT can.
Any advise on how to proceed would be welcome.
Mark Frye
Berkeley Solar Electric Systems
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list