Aluminum vs Copper? [RE-wrenches]
Chris Worcester
chris at solarwindworks.com
Sun Sep 3 07:26:04 PDT 2006
Hi Ron,
This is 3 phase wild AC from the turbine with 3 conductors going to the
Proven ECM2502. The math is different for three phase, you do have an extra
conductor carrying the current. The 2500 watt 48 volt calc comes in at 30.07
amps per phase. These values I quoted you for the 300' distance are using a
3 phase calc.
2% voltage Drop = 4/0 copper
3% VD = 2/0 copper
4% VD =1/0 Copper
5% VD =1 AWG copper
You can use the aluminum if you like, just be sure to use an anti-oxidant on
all connections. I don't use aluminum as I don't feel it's as durable.
Sincerely,
Chris Worcester
NABCEP Certified PV Installer
USA Distributor of Proven Wind Turbines
Toll Free: 877-682-4503
Fax: 530-582-4603
www.solarwindworks.com
chris at solarwindworks.com
"Proven Energy Solutions"
-----Original Message-----
From: Ron Young [mailto:solareagle at solareagle.com]
Sent: Saturday, September 02, 2006 4:26 PM
To: RE-wrenches at topica.com
Subject: Aluminum vs Copper? [RE-wrenches]
Wrenches,
This may have been discussed previously but would appreciate input. I'm
using a long run of wire 2/0 ga. copper would put me right on the line
for 5% line loss (wind turbine @48v approx. 52 amps max. output, 2.5kw)
. 4/0 aluminum would be about 6.3% voltage drop according to my
calculations. The aluminum is a much bigger piece of wire but less than
half the price. Any comments on working with one vs. the other?
Ron Young
Solareagle
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list