Actually Phil is correct as usual, but having recived
many a shock by being grounded and touching energized
equipment, I prefer to have the equipment connected to
a ground rod ALSO.  A seperate structure does not have
to have a bonding jumper back to the main service. 
However I prefer to use one.  

One thing that is needed in these cases is a grounding
system, i.e. a ground rod and other ground means.  In
the case of a pole mount the foundation (when set up
as a Uffer ground) and a ground rod can fullfill 
these requirments.  Having two ground points will
allow them to be connected and a ground test can be
made on this arraingment.  I have measured less than
0.1 ohms between ground rods, and of course as high as
3000 ohms.   

Thanks Phil for correcting and making these
installations safer.  

darryl   

--- Phil Undercuffler <p.undercuffler at conergy.us>
wrote:

> 
> Darryl Thayer said <snip> 
> As I see it the ground rod on a PV array is for two
> purposes, .... Two to
> protect grounded people from any errant
> voltages/currents that they might
> contact during fault conditons.  (part two is what
> the electrical inspector
> is looking for).....
> 
> Actually, this is one function the ground rod does
> NOT perform.  The bonded
> conductor (neutral or negative, generally) provides
> the return current path
> for any fault current, which trips the fuse or
> breaker thereby clearing the
> fault.  
> 
> If you make a short between hot to ground (Please
> don't attempt this at
> home), the breaker will trip no matter whether the
> ground rod is connected
> or not.  However, if you remove the bond between the
> grounded conductor and
> the equipment ground, the breaker won't trip no
> matter how many ground rods
> you drive, thereby presenting potential voltage
> hazards to your grounded
> people--and we all know how hard it is to find well
> grounded people
> sometimes, so you don't want to waste them ;-)
> 
> 
> Please note new phone extensions
>  
>
---------------------------------------------------------
> Phil Undercuffler
> Technical Service Manager, ext. 0741
> Conergy, Inc.
> 1730 Camino Carlos Rey Suite 103
> Santa Fe NM  87507 USA
> Tel 505-473-3800 ext 0741
> Fax 505-473-2134
> www.conergy.us
>
---------------------------------------------------------
> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
>
> 
> 
> 
> 
> 


__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
See the hottest games before your friends! Sign up with Ubisoft, 
and you'll get access to exclusive game news, contests, promotions, 
community forums, and more. It's easy, free, and secure.
http://click.topica.com/caaePuxbz8Qcsbz9JC9f/ Ubisoft
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-wrenches mailing list