ground rod question [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Sun May 21 06:37:26 PDT 2006
Hello Peter
Below is my understanding of the codes regrading
grounding. I have certainly been wrong in the past
and have had many discussions with inspectors on
grounding.
As I see it the ground rod on a PV array is for two
purposes, One to divert any lightening induced surges
to earth protecting your equipment and Two to protect
grounded people from any errant voltages/currents that
they might contact during fault conditons. (part two
is what the electrical inspector is looking for)
For part one The shorter the ground lead the better.
and this is not NEC but NFPA 780 78? the lightening
protection code. The connection should have only
radius bends, and a larger outside diameter and of
course a good ground connection. Y0our array will act
as a capacitor with the sky and as lightening
discharges occur within the county the sky earth
changes potential and your array will have differing
amounts of energy to dissipate. I always drive two
ground rods and separate them by there sphere of
influence 8 to 10 feet.
In case two the grounding is to protect against any
"generated fault currents" currents from the PV system
or back feed through the system from the Utility or
other source that should happen to get on the frame.
This is the one that the inspector is concerned with.
You have a separately derived system and it needs a
grounding electrode system. You can either bring the
ground wire back to the service location and ground
the array with one rod or ground with two rods at the
array. I ALWAYS GROUND AT THE ARRAY AND BERING BACK A
GROUNDING WIRE. When wiring a garage for example the
ground rod is always placed
Hope this helps and is correct.
Darryl
--- Peter Duchon <info at asappower.com> wrote:
>
> What is the max. distance an 8' ground rod can be
> from a ground mounted
> array? Or where is considered best placement for
> ground rods on
> ground-mounted arrays? Ok, that's plural, two
> questions. Pertinent NEC
> 2005 section would be great if anybody has that info
> handy otherwise.
>
> Thanks,
> Peter
> asappower.com
>
> --
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.1.392 / Virus Database: 268.6.0/342 -
> Release Date: 05/17/2006
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list