Low electrolyte levels (was: More on battery management) [RE-wrenches [RE-w
Jay Peltz, Peltz Power
jay at asis.com
Wed May 10 22:17:23 PDT 2006
<x-flowed>
HI Rob,
I have seen more battery mysteries with Surrette's than any other
battery.
I have seen lots of batteries that don't seem to hold charge, won't
come up to charge, etc.
I know that the common fix's, and tests that work with other
batteries just dont seem to do the same thing with Surrettes'
jay
Peltz Power
On May 10, 2006, at 11:09 PM, Rob Harlan wrote:
>
> Windy and Company
>
> We have been scratching our heads over a particular battery mystery:
> It is an installation with eight new (now 4 months old) Surrette
> 530AH 6V
> in 24V config.
> We first were alerted that the Trimetric state of charge readings were
> consistently sustantially over optimistic in relation to both
> voltage and
> specific gravity data. This had resulted in maybe 3-4 weeks during
> which the
> batteries stayed at pretty reduced charge levels. The specific
> gravity
> readings at this point showed a .020 spread between cells.
> Since these were new batteries we suspected the Trimetric or the
> wiring. We
> proceeded to verify Trimetric settings as well as voltage and amperage
> calibration (all OK), tighten all connections to the shunt, verify
> that all
> amperage in and out was passing through the shunt, and insure that
> the owner
> was bringing the batteries to 100% State of Charge ( based on 29.2V
> and 10
> amps) every 5-10 days so the Trimetric has the opportunity to
> recalibrate
> itself. We also installed a second Trimetric closer to the
> batteries to
> provide comparative data (identical). At this point we don't think
> it is the
> Trimetric.
> Upon discovering the undercharged batteries with a 20 point sg
> spread we
> assumed a sulfated condition and
> initiated a generator-driven corrective equilization charge
> (bringing the sg
> to 1.265 and holding the
> batteries there for three hours). This resulted in a reduction of
> the cell
> spread to
> .013.
> The next two and a half months consistently showed:
> 1) Very inacurrate Trimetric state of charge readings (still
> optimistic).
> 2) A variance of 10 to 40 points in cell sg numbers.
> During that 21/2 months we carried out two more equilization
> charges. The 40
> pt spread has ocurred most recently.
> SG readings are being taken with a refractometer which, by the way,
> we find
> to be far easier to use than a hydrometer (order from
> http://www.misco.com/traditional-hand-refractometer.html Glycol and
> Battery
> Tester $135 part # 7084VP+)
> The spread in cell readings do not reveal one outstandingly bad cell.
> Unfortunately baseline specific gravity readings were not taken at
> installation. We have not been physically stirring the electrolyte
> before
> taking refractometer readings. The other possibly pertinent
> information is
> that the cells were slightly overfilled at installation with some
> degree
> of electrolyte (probably not a lot lost during early charging cycles.
>
> Can these symptoms be indicative of a a low acid condition?
> Wouldn't a
> low acid condition prevent the sg readings from reaching 1.270?
> How does
> one determine electrolyte pH? Can a loss in electrolyte cause these
> symptoms? Any other thoughts on this chronic wierdness?
> Thanks in advance for this whole battery discussion and I look
> forward to
> Windy's article.
>
> Rob Harlan
> Harlan Electric
> NABCEP Certified
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list