Bill:


Why is it necessary that the sub have a main breaker?

William











>William,
>
>As long as the subpanel has a main breaker, rather than a main lug panel, it
>should be fine to tap the feeder between the meter main and the sub.
>
>Bill.
>
>
>-----Original Message-----
>From: William Miller [mailto:wrmiller at charter.net]
>Sent: Monday, January 23, 2006 9:25 PM
>To: RE-wrenches at topica.com
>Subject: Popint of connection 30Kw system [RE-wrenches]
>
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Shopping for a new car?
>Pay 2-3% below invoice on a new car of your choice.
>Save thousands with our free car discount finder service!
>http://click.topica.com/caaemrqbz8QcsbaaVcJa/Dealix
>-------------------------------------------------------------------
>
>
>
>
>
>Friends:
>
>I had just asked the question referred to below and received your gracious
>answers when I was called out today to look at installation of a 30KW
>residential system.  This translates to over 100 AAC.  The meter main is a
>CH HP404040SHA,
>(http://www.ch.cutler-hammer.com/unsecure/cms1/TB00500001E.PDF  page 73) a
>400 amp meter main combo with two 200 A main breakers.   One feeds a 200 A
>buss and one feeds a remote sub panel.
>
>There is no combination that allows me to feed 125 A into the 200 A
>buss.  The inverter current, rated up for continuous duty is 170.45 (at 220
>VAC).  The buss rating times 1.2 is 240.  This allows me a 70 A breaker
>which won't even handle the PV generation current.
>
>I'm not sure I can tap the conductors between the meter socket and the buss
>bars, they are very short, bent into a curve and they are part of a listed
>assembly.
>
>Wait, I think I just now got the answer!  There will be a 200 A feeder from
>the second main to a sub-panel.  How about if I tap the conductors going to
>the sub?  This way I'm not feeding a buss and I don't have to tap between
>the meter and the buss.  Any comments?
>
>William Miller
>
>

--
[Non-text portions of this message have been removed]

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Shopping for a new car? 
Pay 2-3% below invoice on a new car of your choice. 
Save thousands with our free car discount finder service!
http://click.topica.com/caaemrqbz8Qcsbz9JC9f/Dealix
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>



More information about the RE-wrenches mailing list