Peter,
Your LADWP ESR may be able to help. DWP has approved several systems with PV30208 inverters. I've seen a lot of PV systems in southern California and have never seen a disco between the inverter and xfmr. Perhaps the inspector can to point you to a system with a disco that he signed off on so you can take a look at what he wants. I agree that it is good to be non-confrontational. but if an L.A. inspector is wrong and won't budge, it's woth talking to his boss. Sometimes it comes to that in L.A.
Joel Davidson

-----Original Message-----
From: peter.parrish at calsolareng.com
Sent: Jun 19, 2005 12:40 PM
To: RE-wrenches at topica.com
Subject: RE: Xantrex PV30208 Install in LA [RE-wrenches]

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get a Free Sirius Satellite Package, don't pass on this!
http://click.topica.com/caadAcobz8Qcsbc0WJAa/ProductTestPanel
-------------------------------------------------------------------

Joel. 

Right now I am trying to gather facts and inspection histories that 
would provide me with a compelling case for treating this system as a 
single derived power source. If you have anything along these lines, I 
would be greatful. I do not, however, think it would be useful to get 
third parties directly involved with the inspection or the inspector.

- Peter

Joel Davidson wrote:
> 
> Peter,
> You got it right. The listed inverter and recognized isolation 
> transformer 
> are a kit. What is the inspector's name?
> Joel Davidson
> 
> ----- Original Message ----- 
> From: <peter.parrish at calsolareng.com>
> To: <RE-wrenches at topica.com>
> Sent: Friday, June 17, 2005 12:16 PM
> Subject: Xantrex PV30208 Install in LA [RE-wrenches]
> 
> 
> Your free subscription is supported by today's sponsor:
> -------------------------------------------------------------------
> Erase wrinkles without painful injections with Nexiderm SP.
> Nexiderm SP is clinically proven to reduce wrinkles by 68% Click
> here to get your 30-day free supply.
> http://click.topica.com/caadAclbz8Qcsbc0WJAa/Nexiderm
> -------------------------------------------------------------------
> 
> We recently finished installation of a 36kW-STC grid-tied PV system in
> the City of LA and encountered some difficulty with our Building and
> Safety inspector wrt the Xantrex PV30208 with 208Y/480Y isolation
> transformer.
> 
> We purchased a "grid-tied kit" from Xantrex which consisted of a PV
> combiner box, DC disconnect, inverter, transormer and AC disconnect.
> 
> It was our understanding that the inverter/transformer was a single
> power source and had been tested to UL1741. We provided a continuous
> ground from the inverter chassis ground stud, to aisolation tranformer
> chassis ground to a cold water pipe; and we furnished the wiring between
> the inverter and transformer via a short section of 1-1/4" EMT.
> 
> Our inspector wanted to treat the inverter and isolation transformer as
> seperately derived power sources with separate grounds to a cold-water
> pipe and an additional fusible disconnect between the two.
> 
> I have spoken to the Xantrex Project (Product) Engineer as well as the
> Manager, Quality Systems for the PV seriews inverters and they have
> provided documentation to support the contention that the inverter and
> transformer comprise a single "system kit" that has been tested and
> certified by UL to be in compliance with UL1741 as well as
> IEEE-929-2000.
> 
> I am prepared to do as the B&S inspector requires, but I would also like
> to know if anyone else has encountered this problem or a similar one in
> connection with the PV30208 inverter.
> 
> - Peter Parrish
> 
> Your free subscription is supported by today's sponsor:
> -------------------------------------------------------------------
> Need a Laptop? Get a Sony Vaio Laptop Free!
> http://click.topica.com/caadAcrbz8Qcsbc0WJAf/ProductTestPanel
> -------------------------------------------------------------------
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios: www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 
> 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without Botox! Nexiderm SP is clinically proven to 
reduce wrinkles by 68% Click here to get your 30-day free supply.
http://click.topica.com/caadAckbz8Qcsbc0WJAf/Nexiderm
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without Botox! Nexiderm SP is clinically proven to 
reduce wrinkles by 68% Click here to get your 30-day free supply.
http://click.topica.com/caadAckbz8Qcsbz9JC9f/Nexiderm
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-wrenches mailing list