interior DC runs [RE-wrenches]
Ryan Mayfield
ryan at energyoutfitters.com
Thu Dec 22 14:43:25 PST 2005
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Is your computer freezing up or slowing down?
Repair corrupt files and harmful errors - protect your PC
Take a 2-minute PC health check-up at no charge!
http://click.topica.com/caaegt3bz8Qcsbz9JC9a/PC PowerScan
-------------------------------------------------------------------
Peter,
Can you clarify why you say the DC disconnect needs to be on the outside
of the building? Section 690.14 indicates the disconnect can be inside
the nearest point of entry. There is also an exception there that
directs you to 690.31(E) that allows you to run through metallic conduit
to the first readily accessible disconnect.
What am I missing?
>The DC disconnect must be on the _outside_ of the building shell.
>- Peter
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Save up to $1,500 on your phone bill with Packet8
Free Activation, Free Equipment & First Month Free!
30-day money back guarantee. 1-877-868-1135
http://click.topica.com/caaegt4bz8Qcsbz9JC9f/ TMONE
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list