Hi All;

I agree Allan. The Square D data bulletin is also very informative. 
Basically Arc fault breakers trip like regular breakers , 20 amp, 5 
minute time delay for instance. But the Arc fault feature also shuts the 
breaker off on an instanteneous surge of 75 A  or higher (line to 
nuetral). Basically higher amp quick duration shorts can cause a fire  
before the regular time delay breaker would trip.  AFCIs have a third 
mode that they will trip (line to ground) which is at 5 amps or less.
Basically, the whole house is protected from any surges over 50 amps by 
the inverter, so the house is actually safer, and Iwould say there would 
even be a possibility of exempting some solar powered homes from the Arc 
Fault breaker rule, if you can prove your power supply can't  surge over 
75 amps.
I think it would take a lot of donuts to get our inspector to go that 
far, maybe at least he'll back off enforcing this test.  The logic is on 
our side:  surely we wouldn't want more surge capacity in order to trip 
the protection against high surges.....Kind of like flunking a golf cart 
in a crash test, because it can't reach crash speed.

Ray


>
>Ray,
>It seems to me that if the inverter can't produce enough to operate a
>tester, the inspector has to allow the home to pass without the test. I cite
>two Code sections to support this:
>690.3 says that in case of conflicting Code sections, 690 trumps.
>690.10(A) specifically allows an inverter to supply current at levels below
>the AC disconnect rating.
>Therefore the Outback (and any listed inverter) passes, even if it can't
>supply 70 amps AC.
>Now, how are you fixed for doughnuts?
>Allan at Positive Energy
>
>
>
>Is anyone having trouble with Arc Fault Breakers not working correctly
>on Outback Power Inverters? The electrical inspector has flunked 2 jobs
>(not our work) because his special tester isn't properly tripping the
>Homeline brand AFI breakers for the bedroom circuits. The electrician
>told me they work fine with their onboard self test.
>Is this a problem with the Inspector's tester, the breaker, the
>inverters, grounding/ bonding or.....????
>
>Thanks for any feed back,
>
>Ray Walters
>
>Y-
>
>
>
>  
>

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Is your computer freezing up or slowing down?
Repair corrupt files and harmful errors - protect your PC
Take a 2-minute PC health check-up at no charge!
http://click.topica.com/caaegt3bz8Qcsbz9JC9f/PC PowerScan
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>



More information about the RE-wrenches mailing list