Darryl,
Starting with a better quality unit, that can be counted on to deliver continuous output, figure inverter maximum (or desired) AC input, divided by (deration for elevation above sea level times deration for how close to maximum rated output we want to run it). 

For elevation deration we use mfgr's specs, or 3.5% per 1,000 ft above sea level if no mfgr's specs.

Example: An Outback VFX can take a maximum of 19A AC in, I believe. At 6,000 feet that's 3.5 X 6 = 21%; 100 - 21 = 795, or 0.79. If I want to run the gennie at no more than 85% of maximum output, then:

____19___
0.79 X 0.85  =  28.3A @ 120V, or at least 3,400 rated watts.  

Then adjust for other factors, like 120V output availability; if 120/240 only you need a step-down transformer, with its attendant losses; reputation of the generator for hangin' in there when you work it that hard; wire losses, if distance is involved, and power factor. Inverter efficiency doesn't play directly into this equation, as it more affects DC output. 

On a big off-grid system we are doing, two VFX3648s, using "Outback stacking" with the Hub, is plenty to run the house and barn. However, we are using a Quad Stack in order to get the charging C/ rate up high enough; the other two inverters are just for charging. At 6,500 feet, we need 18kW including derations, and are using an Onan RS20000 unit.

Hope this helps.
Allan @+E

----- Original Message ----- 
From: "Darryl Thayer" <daryl_solar at yahoo.com>

> What logic process do you use to size a generator?  If
> the generator is oversized and runs at part load its
> effiecency is affected, also my customer is afarid of
> diesels in cold minnesota climate and would perfer a
> propane generator.  

[Non-text portions of this message have been removed]

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Make phone calls with phone service from Packet8.Order VoIP
today & get Free Activation, Free Equipment & First Month 
Free! Packet8 30-day money back guarantee. 1-877-868-1135
http://click.topica.com/caaegt4bz8Qcsbz9JC9f/ TMONE
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list