Hi Wrenches,
I have been working on this same issue with John Wiles. Here is John's
response to this question.
Randy
Positive Energy
-----------------------------------------
Randy and Marco:
Yes, the supply (line) side of the 200 amp existing service
disconnect is the place to connect IAW 690.64(A).
I don't believe tap rules apply since this is not a load circuit or a
feeder.
Use the largest conductors your 100-amp disconnect will accommodate
between the disconnect and the splice. Make them as short as
possible and put them in RMC. Follow general service entrance
requirements as this is what you are connecting to the system.
I assume that you have done due diligence in sizing any inverter
combining load centers IAW 690.64(B)(2).
-----------------------------------------------
-----Original Message-----
From: Marco Mangelsdorf [mailto:marco at pvthawaii.com]
Sent: Tuesday, June 14, 2005 12:53 AM
To: RE-wrenches at topica.com
Subject: disco lug landing [RE-wrenches]
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without painful injections with Nexiderm SP. Nexiderm SP
is clinically proven to reduce wrinkles by 68% Click
here to get your 30-day free supply.
http://click.topica.com/caadAclbz8QcscgAHoHa/Nexiderm
-------------------------------------------------------------------
I've got a non-residential PV application where the only reasonable
utility tie-in location is the existing 200A fused main service
disconnect. I'm going to use a 100A AC fused disconnect which will
carry the combined output of several inverters. The question is: where
to land the output of the 100A inverters' disco--on the line or load
side of the existing 200A main service disco? 'Seems to me it ought to
be on the line side of the 200A disco since if it was on the load side,
there would be the potential to feed 300A through load-side conductors
that were spec'ed to carry only 200A. Following the tap rule in the NEC,
which specifies the conductor size when making such a tap, I don't see
any problem in tapping into the line side...unless I'm missing
something...
Marco Mangelsdorf
President
ProVision Technologies, Inc.
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile www.provisiontechnologies.com
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without Botox! Nexiderm SP is clinically proven to
reduce wrinkles by 68% Click here to get your 30-day free supply.
http://click.topica.com/caadAckbz8QcscgAHoHf/Nexiderm
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get $1,000 to spend on groceries
any way you please. Click here!
http://click.topica.com/caadAcAbz8Qcsbz9JC9f/GrocerySpree
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list