Series fuses/combiner boxes [RE-wrenches]

John Berdner jberdner at sma-america.com
Mon Nov 1 12:04:24 PST 2004


 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get your Golden Tee CD ROM on us
http://click.topica.com/caacOlvbz8Qcsbz9JC9a/PermissionData
-------------------------------------------------------------------

Bill / Wrenches:
 
Contrary to claims made by others: 
UL does not have a Standard to certify no backfeed at the moment.
 
We developed one with J. Wiles that UL approved.
UL does not have an array so we had J. Wiles run the test for us.
Test set up:
2 parallel arrays of series connected modules connected to an
inverter.
Current sensors on each array positive and inverter positive
connection.
 
 
With inverter operating and then again in off state:
Short each inter-module series connection to PV negative 
Measure currents in each case.
Short each iner-module series connection to PV positive.
Measure currents in each case.
 
There is some discussion now re: passing the above test with a single
component failure in the inverter, e.g. a shorted current sensor.
We will see if this part ends up in the next version of UL 1741.
 
Best Regards,
 
John Berdner


>>> billb at endecon.com 10/31/2004 02:43:27 PM >>>


Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get your Golden Tee CD ROM on us
http://click.topica.com/caacNoDbz8QcsbAs9Tla/PermissionData 
-------------------------------------------------------------------

Gary and Darryl,

Without going into a long and confusing explanation, any
crystalline-silicon
module on the market today requires series fusing when 3 or more
strings are
connected in parallel. Use the max series fuse rating on the back of
the
module for simplicity and fuse longevity.

The assumption about 1 or 2 strings is that the inverter is listed to
provide no backfeed current. I believe UL 1741 is being adjusted to
test for
this, but I have not seen much in the way of bulletproof documentation
from
any manufacturer on this subject of no backfeed current. Maybe some of
the
manufacturer reps can chime in here. When I say "bulletproof", I mean
that
it is undeniably clear that UL has evaluated and tested this function
of the
inverter so that the pickiest inspector is satisfied with the
documentation.

Blocking diodes are not required by the code unless the manufacturer
requires their use with their modules. Blocking diodes can not be used
in
lieu of fusing in PV arrays. They should not be used unless you know
what
you are doing.

Bill.


-----Original Message-----
From: Darryl Thayer [mailto:daryl_solar at yahoo.com] 
Sent: Sunday, October 31, 2004 5:38 AM
To: RE-wrenches at topica.com 
Subject: Re: Series fuses/combiner boxes [RE-wrenches]

HI Gary
I went through th e very same question last summer.
For series strings, you can place in series as many
panels your charge control/inverter or module voltage
will allow. This calculation is the Voc/module x
number of modules x 1.25 (code safety factor) x Temp
correction factor (the temp diff from 25C to the 99%
probability not this cold local temp=DT i.e 1+.05*DT)
This is the voltage calculation and it must be less
than 600 volts or the limit of the
controller/inverter.

For Parallel strings John Wiles has a white paper
which says the max current through the module from all
sources must not exceed the max series fuse limiting
that current. That is the max of the Isc of all
parallel collectors or other equipment must not exceed
the max series fuse as labeled on the module.

As an example if you have two modules in parallel each
of 3 amps Isc, and the fuse protection is 2 X 3 x
1.25= 7.5 amps And if one modules fails and the
second module supplies Isc the first module could see
3 amps plus 7.5 amps reverse current through the fuse
or the failed module would have 10.5 amps. To comply
with the code the module must have 10.5 max fuse size.


This is very limiting of course. And I have wondered
the use here of reverse diodes. Either at the breaker
or on each module. The second solution is to fuse
each module at the junction box.

Now it is my turn. What is the ruling on Blocking
Diodes? What is the accepted fuse holder that can be
installed in module junction boxes?

Thanks Daryl

--- Gary Higbee < gary at windstreamsolar.com > wrote:
> Wrenches,
>
> I'd appreciate some help in determining when we need
> fuses or breakers for
> parallel strings. For some reason I thought that two
> strings in parallel are
> OK, but that for three and above we need to use the
> appropriate combiner box
> with breakers or fuses. This feels too
> vague--especially as I am now being
> asked to review and approve systems (for the Energy
> Trust of Oregon) with
> more than two parallel circuits.
>
> Please shed some photons on this--when do we not
> need and when do we need
> parallel string fuses or breakers, and where does
> this correspond to in the
> code--or make common sense?
>
> Thanks so much!
>
> Gary

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Your Neighbors will envy your Garden when you get 100 bulbs on us
http://click.topica.com/caacNoJbz8QcsbAs9Tlf/PermissionData 
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com 

Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read 

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php 

Check out participant bios: www.mrsharkey.com/wrenches/ 

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com 





--
[Non-text portions of this message have been removed]

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Are you serious about buying a NEW car or truck soon? 
Research before stepping on the car lot and save THOUSANDS!
Get NO OBLIGATION price quotes from car dealers in your area.
http://click.topica.com/caacOlPbz8Qcsbz9JC9f/LeadClick
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-wrenches mailing list