net-metered efficiency observations [RE-wrenches]

Kurt Nelson sunwise at cheqnet.net
Thu Mar 18 14:35:46 PST 2004


Bill and Kirk,

The night time losses are related to battery size and condition.  If
Kirk is seeing 1KWH it probably has a large battery.  BTW, I still have
a couple SW systems out there with Sharkey's "work around" that work
great!  Disconnect that SW at night even though it is not smart enough
to do it on its own!

Kurt Nelson

-----Original Message-----
From: Bill Brooks [mailto:billb at endecon.com] 
Sent: Thursday, March 18, 2004 3:26 PM
To: RE-wrenches at topica.com
Subject: RE: net-metered efficiency observations [RE-wrenches]

Kirk,

You mentioned that you have set the sell voltage to 52 Volts. Why is the
sell voltage even being used if this is a net metered system? Normally
we
just set the float voltage to 53.6 V (depending on the battery) since
this
is temperature compensated. The sell voltage is not temperature
compensated.
Although it may be an okay voltage to keep the battery at year-round,
regardless of how well controlled the battery temperature is, it should
be
temperature compensated in my view.

You mention that the you think the conversion efficiency is too high.
What
are you expecting? I would say that it could be low. Typical nighttime
losses should be .5 to .8 kWh since the unit draws about 50 Watts all
night.
Does the MX60 measure power output or power input?

Bill.

-----Original Message-----
From: Kirk Herander [mailto:kirk at vtsolar.com]
Sent: Thursday, March 18, 2004 12:38 PM
To: RE-wrenches at topica.com
Subject: Re: net-metered efficiency observations [RE-wrenches]


Todd, The readings were dawn to dusk, and this inverter eats about 1kw
of
grid power overnight.

Vermont Solar Engineering
Kirk Herander
North American Board of Certified Energy Practitioners
Certified Solar PV Installer(TM)
Xantrex Certified Dealer Charter Member
NYSERDA-eligible installer
Vermont Solar and Wind Partner

PO Box 697
Burlington, VT. 05402
www.vermontsolar.com
www.backeastsolar.com
800.286.1252 - 802.863.1202
fax 802.863.7908

----- Original Message -----
From: "Todd Cory, Mt. Shasta Energy Services"
<toddcory at finestplanet.com>
To: <RE-wrenches at topica.com>
Sent: Thursday, March 18, 2004 3:18 PM
Subject: Re: net-metered efficiency observations [RE-wrenches]

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------









More information about the RE-wrenches mailing list