EMT - UL Heads Up [RE-wrenches]
Bill Brooks
billb at endecon.com
Wed Mar 17 15:06:59 PST 2004
XHHW-2 is a conduit wire. Occasionally USE-2 is also labeled XHHW-2 so that
it can be run in conduit as well. The reason LA is suggesting XHHW-2 is that
THWN-2 was hard to find about a year or so ago. Now, depending on the
supplier, it can be found a Home Depot in sizes down to 14 AWG.
Bill.
-----Original Message-----
From: Jason Fisher [mailto:jfisher at nahbrc.org]
Sent: Wednesday, March 17, 2004 2:17 PM
To: RE-wrenches at topica.com
Subject: Re: EMT - UL Heads Up [RE-wrenches]
XHHW Should be marked "sunlight resistant" or similar to be used outside
of conduit correct?
USE has similar qualities but is listed for direct sun exposure. Some
XHHW is also marked USE.
Jason Fisher
-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Wednesday, March 17, 2004 3:26 PM
To: RE-wrenches at topica.com
Subject: [SPAM] - Re: EMT - UL Heads Up [RE-wrenches] - Email found in
subject
In Los Angeles we use XHHW-2.
Original Message:
-----------------
From: Mark Byington markbyington at sbcglobal.net
Date: Wed, 17 Mar 2004 07:57:05 -0800
To: RE-wrenches at topica.com
Subject: Re: EMT - UL Heads Up [RE-wrenches]
"... so what about using USE wire in EMT? They can't argue about the
wire getting wet?? ( or for that matter the THWN)"
Most inspectors we deal with (SF bay area) require all conductors in
outdoor EMT to be 90 degree C and wet rated. This means USE-2 or
THWN-2.
Mark
Cobalt Power Systems, Inc.
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--------------------------------------------------------------------
mail2web - Check your email from the web at http://mail2web.com/ .
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list