EMT - UL Heads Up [RE-wrenches]
Jay Peltz, Peltz Power
jay at asis.com
Tue Mar 16 18:07:31 PST 2004
I've got a suggestion that I wonder would work?
I too don't really like PVC for horizontal runs, so what about using USE
wire in EMT? They can't argue about the wire getting wet?? ( or for that
matter the THWN)
In colorado the inspectors are requiring expansion couplings on all PVC that
connect from ground to above ground. Makes sense.
Jay
Peltz Power
----- Original Message -----
From: "Jason Fisher" <jfisher at nahbrc.org>
To: <RE-wrenches at topica.com>
Sent: Tuesday, March 16, 2004 7:34 AM
Subject: RE: EMT - UL Heads Up [RE-wrenches]
> A not so often followed NEC requirement is to provide expansion fittings
> on longer PVC runs (NEC 1999 347-9, don't have 2002 with me). These
> fittings (slip coupled pipe with o-rings and Vaseline, that are still
> not "watertight"!) are hard to find in supply shops but are essential
> for applications like wiring piers. Generally, I'd hope we keep our runs
> shorter but one still should keep in mind just how much this stuff moves
> over temperature swings (see table). Frequently, you'll find pipes
> popped out of glued connectors at enclosures. While one might blame the
> helper for not putting enough glue on the joint, often times this is due
> to the conduit being installed during the hot summer, strapped down
> tight, then shrinking during the winter. You also see this a lot when
> PVC comes out of the ground, especially if it wasn't supported by
> undisturbed earth. And yes, all the old PVC I've messed with shatters
> easily.
>
> It is sad to hear that the rumors of this EMT-fitting issue are now
> being played out in CA. I do not look forward to the day when inspectors
> here start pulling this out of their hats. Anyone who has done
> electrical service work on equipment in wet applications knows that no
> conduit system is watertight, even the expensive PVC coated steel. The
> conductors need to be rated wet for a reason and we have always drilled
> weep holes in our exposed boxes. I had an inspector once, take issue
> with this (not in line with the box's listing) and suggest that we
> rather leave out a threaded plug and install screening to keep out the
> bugs. Huh? OK, thanks for the tip. I said I'd make sure I did that "next
> time".
>
> Jason Fisher
>
> -----Original Message-----
> From: William Miller [mailto:wrmiller at slonet.org]
> Sent: Monday, March 15, 2004 10:27 PM
> To: RE-wrenches at topica.com
> Subject: [SPAM] - RE: EMT - UL Heads Up [RE-wrenches] - Email found in
> subject
>
> At 06:08 PM 3/15/2004, you wrote:
>
> >I don't know if my experiences come from UV or heat-related exposures,
> >or a combination thereof. What I do know is that I have seen and
> >replaced too many exposed horizontal PVC conduit installations with
> >sagging runs, split fittings, disfigured shapes, separated connections,
>
>
> That's easy to fix! Just strap the PVC to some EMT!
>
> William
>
> PS: With PVC you can't ignore thermal expansion effects. (Not so
> familiar with EMT-- Is this also an issue?) I don't ever figure any
> pipe, on a roof or underground, will stay dry. And it's true, PVC can
> sag, it requires better support than EMT.
>
> Wm
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list