Hi y'All
Trident Energy Systems has several hundres apartments and several dozens
of houses working for 20+ years with this kind of system. Search on
Trident Solar for more information.
Deant
Darryl Thayer wrote:
>HI dan
>When I copied and published the idea in 1993, I copied
>a paper by someone else, who I think copied another.
>University of Wisconsin at Madison has also published
>on the topic.
>
>Daryl
>
>--- Dana Orzel <dana at solarwork.com> wrote:
>
>
>>Hey there Travis,
>>
>>How about pouring a 4" to 6" Insulated slab with
>>WIRSBO or eq. radiant heat
>>tube in the slab, viwalah - NO TANK REQUIRED. You
>>are already pouring a slab
>>why not put it to work for you twice. Contact me off
>>list or call to
>>discuss. This concept I call SDI - Solar Direct
>>Injection PV pumped solar
>>heated water from a shw collector direct into the
>>slab with a backup heat
>>source paralleled into the slab. I wish I could take
>>credit for the concept
>>and origination but Bristol Stickney in NM is the
>>man to whom I credit with
>>this.
>>
>>Responsible Technologies for Responsible People.
>>Great Solar Works, Inc.
>>dana at solarwork.com - 970.626.5253
>>Ridgway, CO, USA
>>
>>----- Original Message -----
>>From: "Travis Creswell, Ozark Solar"
>><ozsolar at ipa.net>
>>To: <RE-wrenches at topica.com>
>>Sent: Saturday, March 06, 2004 9:41 AM
>>Subject: Solar Space Heating Storage Tank Size
>>[RE-wrenches]
>>
>>
>>
>>
>>>Hello All,
>>>
>>>I am designing a storage tank (atmospheric) for
>>>
>>>
>>the radiant in floor
>>heating
>>
>>
>>>system for my new shop. The office portion the
>>>
>>>
>>shop will be constructed
>>of
>>
>>
>>>Insulated Concrete Forms (IFC's) with a concrete
>>>
>>>
>>roof. This will allow it
>>
>>
>>>to be also be used as storm shelter. Three
>>>
>>>
>>tornados missed us by less
>>than
>>
>>
>>>5 miles last spring.
>>>
>>>These same forms will make a great tank as they
>>>
>>>
>>are plenty strong and well
>>
>>
>>>insulated. One wall of the storage tank can be
>>>
>>>
>>shared with the office
>>
>>
>>>reducing the number of forms needed for the tank
>>>
>>>
>>and the concrete pump
>>trunk
>>
>>
>>>will already be on site for the office walls.
>>>
>>>
>>I've had an engineer look
>>it
>>
>>
>>>over and he has given it his blessing to build a
>>>
>>>
>>tank up to 8' tall!
>>
>>
>>>Of course I will have to line the tank, which is
>>>
>>>
>>easy enough with EPDM. A
>>
>>
>>>reasonably tight insulated lid will need to be
>>>
>>>
>>constructed as well.
>>
>>
>>>I'll have 400 ft2 of liquid flat plates and a very
>>>
>>>
>>efficient wood
>>
>>
>>>gasification boiler rated at 140,000 Btu's output.
>>>
>>>
>> Does 600 Btu's/ft2/per
>>
>>
>>>day sound right for the solar thermal array? I'm
>>>
>>>
>>thinking that is safe as
>>
>>
>>>here in Southwest Missouri our average winter
>>>
>>>
>>daytime temps are reasonably
>>
>>
>>>mild.
>>>
>>>My main questions are the size and shape of the
>>>
>>>
>>tank. I can build the
>>tank
>>
>>
>>>in any size or shape (tall and skinny vs. short
>>>
>>>
>>and wide for example). In
>>
>>
>>>looking over some of my dated solar books, 2
>>>
>>>
>>gallons per sq ft seems to be
>>
>>
>>>the maximum ratio of thermal collector to storage.
>>>
>>>
>> I assume that "rule of
>>
>>
>>>thumb" was long before the widespread use of
>>>
>>>
>>radiant in-floor heating.
>>
>>
>>>Since radiant in-floor requires lower temps than
>>>
>>>
>>baseboards or forced air
>>is
>>
>>
>>>it acceptable (or required) to use a larger
>>>
>>>
>>storage tank?
>>
>>
>>>I've built a very detailed spreadsheet that allows
>>>
>>>
>>me to see how long it
>>
>>
>>>will take to "recharge" various sizes of tanks
>>>
>>>
>>with the solar thermal
>>array
>>
>>
>>>and the wood boiler. The most efficient operation
>>>
>>>
>>of the boiler is to be
>>
>>
>>>fill it with wood then run wide open until the
>>>
>>>
>>wood is gone. If the tank
>>is
>>
>>
>>>not large enough then the boiler will shut down
>>>
>>>
>>and smolder thus lowering
>>
>>
>>>the efficiency of the burn cycle. The spreadsheet
>>>
>>>
>>shows me that one
>>firing
>>
>>
>>>of the boiler will easily charge up to a 1500
>>>
>>>
>>gallon tank. But this size
>>of
>>
>>
>>>tank amounts to nearly 4 ft2 of thermal per gallon
>>>
>>>
>>of storage. One idea
>>is
>>
>>
>>>to build a tall skinny tank. I could place the
>>>
>>>
>>solar heat exchanger
>>higher
>>
>>
>>>in the tank so it has less water to heat. This is
>>>
>>>
>>assuming that
>>
>>
>>>stratification will keep all that heated water up
>>>
>>>
>>near the top. Can
>>anyone
>>
>>
>>>confirm if this is a reasonable expectation? The
>>>
>>>
>>space heating tanks that
>>
>>
>>>I've seen are very short but that might have been
>>>
>>>
>>for structural reasons.
>>
>>
>>>Does anyone have a source for the finned copper
>>>
>>>
>>coils that were commonly
>>
>>
>>>used in these systems? I'd rather use them than
>>>
>>>
>>make my own coils.
>>
>>
>>>Any thought and suggestions are appreciated. I'd
>>>
>>>
>>be glad to share the
>>
>>
>>>spreadsheet and the system diagram should anyone
>>>
>>>
>>want it.
>>
>>
>>>Thanks in advance!
>>>
>>>Travis Creswell
>>>Ozark Energy Services, Inc.
>>>
>>>- - - -
>>>To send a message: RE-wrenches at topica.com
>>>
>>>Archive of previous messages:
>>>
>>>
>>http://www.topica.com/lists/RE-wrenches/
>>
>>
>>>List rules & etiquette:
>>>
>>>
>>http://www.mrsharkey.com/wrenches/etiquete.htm
>>
>>
>>>Check out participant bios:
>>>
>>>
>>www.mrsharkey.com/wrenches/index.html
>>
>>
>>>Hosted by Home Power magazine
>>>
>>>Moderator: michael.welch at homepower.com
>>>
>>>
>>>
>>>
>>>
>>>
>>- - - -
>>To send a message: RE-wrenches at topica.com
>>
>>Archive of previous messages:
>>http://www.topica.com/lists/RE-wrenches/
>>
>>List rules & etiquette:
>>http://www.mrsharkey.com/wrenches/etiquete.htm
>>
>>Check out participant bios:
>>www.mrsharkey.com/wrenches/index.html
>>
>>Hosted by Home Power magazine
>>
>>Moderator: michael.welch at homepower.com
>>
>>
>>
>>
>>
>
>
>__________________________________
>Do you Yahoo!?
>Yahoo! Search - Find what you’re looking for faster
>http://search.yahoo.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
--
* Cooperative Community Energy* *Dean T. Newberry*
430 D Street, Davis CA, 95616
Tel: 530 758-6064
Fax: 530 758-3684
Email: deant at dcn.org
Web: CCEnergy.com
Talbott Solar <http://www.dcn.davis.ca.us/go/deant/>
Contr. Lic. # B-667908
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list