Keith -
You might try larger motor run capacitors - I've put as large as 50uF
caps on SWs in the past to eliminate problems - and it works - but the
idle power consumption of each SW will increase to around 50 watts if I
remember correctly. The capacitors should be wired across each inverter
(neu-hot) not across the 240 VAC output for the best results. Be sure
to disable the search mode when adding the big caps as its not usuable
with them on there - you'll get a real disco effect on the whole house.
There are a few other tricks you can try - but this should work for
you...
Christopher
>I have tried GE 4uf 370 VAC run capacitors to clean the ripple, but it
>seems when the power goes out, and the "19" ceiling fans are on as well
>as the dimmers for the lighting, the lights in some areas start to do
>the disco strobe and some of the fans start to hum.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list