Allan and Dean,
Be very careful about making assumptions about XHHW-2 wire. It has to say
"sunlight resistant" directly on the jacket, or it must be assumed to not be
sunlight resistant. Service entrance and tray cables are the only conductors
that are all tested for sunlight resistance. I have seen XHHW-2 that fell
apart in sunlight. Service entrance cables are also treated with rodent
repellant--tray cable generally is not. I have seen rabbits chew briefly on
USE-2 cable, but they usually only take one or two bites before they have
had enough and turn their attention to the connectors (did I just make
another case for conduit wire--totally unintended I assure you).
With ungrounded systems being allow explicitely in the 2005 code, we need to
see two conductor cables with connectors that are all sunlight and rodent
resistant.
Bill.
-----Original Message-----
From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
Sent: Wednesday, December 15, 2004 8:45 AM
To: New wrenches posting
Subject: New wire for array wiring? [RE-wrenches]
Re: Fw: new wire for array wiring? [RE-wrenches]----- Original Message -----
Much to my suprise, we concluded that XHHW-2 is rated for exposure to=20 the
sun.
Maybe a commentary from John Wiles would be useful at this time.
cul deant
From: John Wiles
To: Allan Sindelar
Sent: Wednesday, December 15, 2004 9:31 AM
Thanks for the forward: Here is a non-answer.
The October 2003 UL Wire and Cable Marking Guide indicates that XHHW and
XHHW-2 as single wires may be sunlight resistant if so marked.
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
We can reduce your unsecured credit card debt by 40-60%.
Dont file bankruptcy. Be Debt Free in as little as 1 year. Take
control of your situation. 100% FREE Consultation.
http://click.topica.com/caacVlYbz8Qcsbz9JC9f/KnockOutDebt
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list