I think this whole thing is just to raise cain and get us to stop using the
flexible cable altogether. He told me in person the only legal cable to use
on batteries is THHN, let that sit in a battery box for a while and see what
happens! When I asked him about it was plain that he didn't want to discuss
it and further.
He didn't seem to think anyone could do a good crimp except the factory,
either.
He specifically mentioned the ends on MC cables.

Bob

RE. Ellison
Supplier of;
Alternative Energy Systems & Supplies
34642 Countryman Road
Theresa, NY. USA
                               13691-2076


-----Original Message-----
From: David Palumbo, Independent Power & Light [mailto:ipl at sover.net]
Sent: Friday, August 27, 2004 9:04 AM
To: RE-wrenches at topica.com
Subject: RE: Flexible Cables: Important Safety Issue [RE-wrenches]




Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Save up to 80% on Inkjet & Toner Supplies. 100% Satisfaction
Guarantee. Free Shipping on orders over $49. www.inksoutlet.com
http://click.topica.com/caacAsfbz8QcsbfmDywa/Inksoutlet
-------------------------------------------------------------------




<<  Yep, that sounds right to me. As far as crimp lugs go, I've always
(well,
maybe not always) used the heavy Magna lugs with three crimps. I got the
crimper years ago from Dave Katz at AEE; one of my favorite tools. Even
though  there are some wire sizes and types that are a real booger to get
into the fittings, particularly the 2/0 welding cable with the 10 zillion
strands, when those babies are crimped - they stay crimped. Not even J.
Wiles could pull 'em out! Maybe. Matt T>>


I also use the Magna lugs with a big crimper (one bench mounted in the shop,
and one portable). I use the glue filled heat shrink tubing to seal out air
(long enough length of heat shrink to insure that it can take the bend in
the cable). If the lug will on (or near) the batteries I smear a little
Vaseline on the lug as well as the battery terminal.

I made a change with my normal install procedure yesterday as a result of
JW's posting. I use a 300A Class T fuse with a Fuse block set up provided by
SunWize. This fuse block is mounted inside the battery box. I ditched the
two Ilsco single lugs and substituted crimped lugs on the 4/0 fine stranded
flex cable. I'm happy with the connections I "think" that they are better
longer lasting connections than the set screw tightened lugs. Cost - two
Magna lugs $ 1.71 ea. Heat shrink tube 6" length of 1" tube (cut in two
pieces)$1.34 so that's less than 5 bucks in parts, add in 15 minutes of
labor.

All the other termination points for the 4/0 flex cable in the Out Back DC
box are done with same crimped lug method. No set screw lugs in the OB
equipment for the big cable.

While I agree with the general nature of Bob-0 and Matt's stance on Wiles
mandates, this one does not seem to be too onerous and it seems to me to be
a better way to make the connection. However, that being said, do I now
revisit all of my past installs done with fine stranded flex cable into set
screw lugs to upgrade?

Dave

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Sponsor a child today through Children International.
Give a desperately poor child hope for a brighter future.
For only $18 a month you can make a difference!
http://click.topica.com/caacvgobz8QcsbfmDywf/ChildrenInternational
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Need cash fast? Get a $500 CASH ADVANCE overnight! Let 
YourCashCentral get you the cash you need.
http://click.topica.com/caacxycbz8Qcsbz9JC9f/MyOnlinePayday
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------

















More information about the RE-wrenches mailing list