Flexible Cables: Important Safety Issue [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Wed Aug 25 08:28:52 PDT 2004
<x-flowed>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Buy Stocks and Index Funds for just $4 No Account or
Investment Minimums and No Inactivity Fees Automatically
invest weekly or monthly and build your future.
http://click.topica.com/caacvggbz8Qcsbz9JC9a/Sharebuilder
-------------------------------------------------------------------
Well, that's old JW all over isn't it? Find a situation that could be
a problem or that is very, very rarely a problem and make Mt Everest
out of a molehill. Since day one of his inputs to the RE industry
everything he suggests or opines that UL/NEC requires raises the cost
of a PV system. EVERYTHING! Ever notice that? This man comes to us
from the nuke industry. I find it damn hard not to question his
motives. He's kind of a Swift Boat PV Opinionater for Arcane Stuff,
ain't he?
Jesus H. Christ!
> Oh my God.
>
> This isn't April 1st is it?
>
> So now all those inverters that we've been putting in with "fine stranded
>wire" for the past 20 years are going to have to have their cables removed
>and exchanged because "there have been problems"? What, fires? Explosions?
>Electrocutions? Befuddled inspectors?
>
> I have to say that in all the years I've been working on battery-based
>inverters, the ONLY connection problems I have observed have ONLY been
>those that had stiffy wire for inverter cables! There is so much potential
>for tension-caused breakage with this method, so many (virtually) impossible
>wire bends and seeming non-compatablity with all the commonly used, tried
>and true connection components, I just can't bel;ieve that this can be for
>real.
>
> If this such a huge problem, why not simply tin the wire ends?! UL indeed.
>
> Matt T
> ----- Original Message -----
> From: "Allan Sindelar" <allan at positiveenergysolar.com>
> To: "New wrenches posting" <RE-wrenches at topica.com>
> Sent: Tuesday, August 24, 2004 3:35 PM
> Subject: Fw: Flexible Cables: Important Safety Issue [RE-wrenches]
> Wrenches,
> Forwarded to this list at the request of John Wiles
>
> ----- Original Message -----
> From: "John Wiles" <jwiles at nmsu.edu>
> Sent: Tuesday, August 24, 2004 3:50 PM
> Subject: Flexible Cables
>
>
> Flexible, Fine-Stranded Cables: Incompatibilities with Set-Screw
>Mechanical
> Terminals and Lugs
>
> Reports have been received over the last several years about field-made
> connections that have failed when flexible, fine-stranded cables have been
> used with mechanical terminals or lugs that use a set screw to hold the
>wire
> in the terminal.
>
> These terminals are found on nearly all circuit breakers (except those
>with
> stud-type terminals), fuse holders, disconnects, PV inverters, charge
> controllers, power distribution blocks, some PV modules, and many other
> types of electrical equipment.
>
> Fine-stranded conductors and cables are considered as those cables having
> stranding more numerous than Class B or C stranding. Class B stranding
>(the
> most common) will normally have 7 strands of wire per conductor in sizes
> 18-2 AWG, 19 strands in sizes 1-4/0 AWG, and 37 strands in sizes 250-500
> kcmil. Conductors having more strands than these are widely available and
> are in different classes such as K and M used for portable power cords and
> welding cables. Commonly used building-wire cables such as USE, THW, RHW,
> THHN and the like are most commonly available with Class B stranding, but
> are also readily available with higher stranding. Fine-stranded cables are
> frequently used by PV installers to ease installation and are used in PV
> systems for battery cables, power conductors to large utility-interactive
> inverters and elsewhere.
>
> Some modules are supplied with fine-stranded interconnecting cables with
> attached connectors. While these crimped-on connectors listed with the
> module are suitable for use with the fine-stranded conductors, an
> end-of-string conductor with mating connector may also be supplied with
>the
> fine-stranded conductor ,and the unterminated end of that conductor will
>not
> be compatible with mechanical terminals.
>
> According to UL Standard 486 A-B, a terminal/lug/connector must be listed
> and marked for use with conductors stranded in other than Class B and C.
> With no marking or factory literature/instructions to the contrary, the
> terminal may only be used with conductors with the most common Class B and
>C
> stranded conductors. They are not suitable and should not be used with
> fine-stranded cables. UL engineers have said that few (if any) of the
>normal
> screw-type mechanical terminals that the PV industry commonly uses have
>been
> listed for use with fine stranded wires. The terminal must be marked or
> labeled specifically for use with fine-stranded conductors.
>
> UL suggests two problems, both of which have been experienced in PV
>systems.
> First, the turning screw tends to break the fine wire strands, reducing
>the
> amount of copper available to meet the listed ampacity. Secondly, the
> initial torque setting does not hold and the fine strands continue to
> compress after the initial tightening. Even after subsequent retorquing,
>the
> connection may still loosen. The loosening connection creates a
> higher-than-normal resistance connection that heats and may eventually
>fail.
> Recent examples of failed mechanical terminals from a large PV system have
> been found. The terminal had been torqued properly less than three months
> before the failure.
>
> Solutions
>
> All electrical equipment listed to UL Standards has:
>
> . Terminals rated for the required current and sized to accept the proper
> conductors
>
> . Sufficient wire bending space to accommodate the Class B stranded
> conductors in a manner that meets the wire bending requirements of the NEC
>
> . Provisions to accept the appropriate conduit size for these conductors
> where conduit is required.
>
> It is therefore unnecessary to use the fine-stranded cables except
>possibly
> when dealing with conductors 4/0 AWG and larger.
>
> In those cases where a fine-stranded cable must be used, a few
>manufacturers
> make a limited number of crimp-on compression lugs in various sizes that
>are
> suitable for use with fine-stranded cables.
>
> Factory-supplied markings and literature indicate which lugs are suitable.
> An example is the ILSCO FE series of lugs in sizes 2/0 AWG and larger.
> Burndy makes a YA series of lugs in sizes 14 AWG and up. In both cases the
> lugs are solid copper. It should be emphasized: Most crimp-on lugs are not
> listed for use with fine-stranded wire. Where the crimp-on compression
>lugs
> can be used, they must be installed using the tools recommended by the
> manufacturer and, of course, they must be attached to a stud with a nut
>and
> washer.
>
> Burndy and others make pin adapters (a.k.a. pigtail adapters) that can be
> crimped on fine-stranded cables. These pin adapters provide a protruding
>pin
> that can be inserted into a standard screw-type mechanical connector.
>Again,
> not all pin adapters/pigtail adapters are listed for use with
>fine-stranded
> conductors; some are intended for use with aluminum wire and others
>provide
> only a conversion to a smaller AWG size for B Class conductor.
>
> It is suggested that the use of fine-stranded conductors be avoided
>wherever
> possible. Where such cables must be used, they should only be terminated
> with the appropriate connectors/lugs. Previously installed systems should
>be
> revisited and the cables replaced where possible or terminated properly.
>
> John Wiles SWTDI/NMSU jwiles at nmsu.edu 505-646-6105
>
> > If I can provide further information, please do not hesitate to call,
> > e-mail or fax me.
> >
> > John
> >
> > John C. Wiles, Program Manager
> > Southwest Technology Development Institute, New Mexico State University
> > 505-646-6105 505-646-3841 (FAX) http://www.NMSU.Edu/~tdi
> > SWTDI/NMSU
> > Corner Research Drive and Sam Steel Way
> > Box 30001/MSC 3 SOLAR
> > Las Cruces, NM 88003-8001
>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
RE-GROW YOUR HAIR STARTING NOW.....Click here for more info!
http://click.topica.com/caacxydbz8Qcsbz9JC9f/Medical Hair Restoration
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list