ratcheting cyclometers [RE-wrenches]
mlafferty at universalenergies.com
mlafferty at universalenergies.com
Thu Jan 15 18:24:39 PST 2004
Doug P said:
> Simple. Using a standard 240v utility meter, wire the 120v leg from
> the SW output to the subpanel so that power passing to the subpanel
> spins the meter forward. Wire the other 120v leg so that power passing
> from the main panel to the SW input spins the meter backwards.
Victor C said:
> I'm still saying night time batter charging should be deducted.
All:
On a single, 120 V inverter, Doug's description should work...
Subtracting nighttime battery charging from the cumulative kWH reading
on the meter. Be sure your inverter neutral is common to ground and
that you connect that to the neutral/ground lug in the meter socket.
Specific 4-Jaw Wiring:
Inverter Output "Hot" Leg to Top Left Lug of Meter Socket.
Sub-Panel "Hot" Feeder Leg to Bottom Left of Meter Socket.
Main Panel Inverter Breaker "Hot" Leg to Bottom Right of Meter Socket.
Inverter AC In "Hot" Leg to Top Right of Meter Socket.
Like Doug, I have not tried this personally but believe it will work to
a suitable degree of accuracy.
Hope this helps!
By the way, I ABSOLUTELY agree with Victor! You can't "have your cake
and eat it too"!
But da**ed be the man that tries to tell me I can't "have my beer and
drink it too"t! LOL
Matt Lafferty
Universal Energies Institute
mlafferty at universalenergies.com
(916) 422-9772
(916) 628-7694 Cell
(916) 914-2247 Fax
www.universalenergies.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list