We typically use single-conductor MC cable. Does this new provision mean
that only sheathed two-conductor MC cable is permitted?
Allan
----- Original Message -----
From: "Bill Brooks" <billb at endecon.com>
William,
Here is the language from the 2005 NEC:
690.35(D) The photovoltaic source and output conductors shall
consist of sheathed (jacketed) multi-conductor cables or
shall be installed in a raceway.