Digest for RE-wrenches at topica.com, issue 1340 [RE-wrenches]
Steve Willey, Backwoods Solar
steve at backwoodssolar.com
Tue Jan 13 13:09:13 PST 2004
On the stacking question, where you have two 12 volt inverters and a 24 volt
bank, I would caution against a DC-DC converter. While these allow taking
12 volts DC applications from a 24 volt bank, we find many converters fail
when the half-tap load is an inverter. This is due to the ripple that is
imposed across the converter which it tries to follow and correct. They run
really hot.
The other solution suggested, changing to different inverters to match the
battery voltage is one way, but a third way: REARRANGE the battery bank to
a 12 volt bank, then use the Outback MX charge control to charge the 12 volt
bank from whatever 24 volt source you have.
Steve Willey,
Backwoods Solar Electric Systems
steve at backwoodssolar.com
Hi All,
Can I stack 2 Sw 2512's into a center taped 24v battery bank?
The reason as I'm sure you are going to ask is a friend with a really large
hydro, we are talking 200 amps at 12v from the hydro. And he is trying to
improve that by going to 24v.
But he already has the SW's, hence the question.
Thanks,
jay
Peltz Power
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list