UPS as a stand alone inverter? [RE-wrenches]
Robert Warren
robertwarren at mail.com
Sat Sep 6 21:58:32 PDT 2003
Doug,
I did a similar thing with two Best UPS's at Rocky Mountain Institute
about 5 years ago. But I used PV to directly charge the batteries, not
another inverter, which I would not recomnend. I removed the internal
batteries of both a 3.1 KVA and a 5.3 KVA unit and hooked the DC battery
bus of both to a huge external Absolyte battery bank. Then I added a
capicitor on the battery circuit as a filter for the PV PWM controller,
and the batteries are float charged by a 2 kW PV array. This arrangement
was designed to provide about 2 days backup for a network of 30
computers.
But you are wrong about one thing--the Best inverter (Ferrups model
UPS) is not on all the time. That is the beauty of this UPS. It is
normally off and only comes on during a brown-out or blackout. it takes
2 to 4 ms for the inverter to switch on. However, as they have a big
ferroressonant transformer between the inverter and the load, the
collapsing magnetic field in the transformer holds up the load VA for a
good 20 ms so that at the computer, you don't see any power flicker
whatsoever.
In my 12 years as a Best service rep, I think these things are pretty
much bullet proof. I rearely had to change out boards, except to upgrade
or change voltage configurations. By contrast, a lot of other UPS's I
serviced had a much higher failure rate. The only thing is, for a
PV-UPS, you have about a 10 to 12% loss due to heat and magnetic
saturation of the ferro transformer. If you can live with that, it is
worth looking into. However, this efficiency is if you are at 70 to 90%
of capacity with your load. If you have a load rated at a lot less than
this, the efficiency goes to hell, as you are on the low end of the
output efficiency curve.
Best got bought out by Exide, which got bought out by Invensys. They
are now made by Exide, I think, but I don't know if they still still
make all models. I think they rebranded it into the Powerware line,
which blurs the technology line of a different type of UPS, which is
Exide's main seller.
Robert Warren
Doug Pratt wrote:
> Has any one tried using a high end sinewave (online, zero transfer time)
> UPS as a standalone inverter?
>
> Bill Loesch
>
>
> I've got some limited experience. Back in the mid-90s Real Goods took a
> pair of Best UPS units, one at 3kva, one at 7kva, that we were already
> using for on-site critical backup, and by adding some separate robust
> battery chargers (Trace SW-series inverters) and some funky
> non-auto-starting generators, we made ourselves a couple of pretty
> robust UPS systems. The Best inverters are always on. Normally they
> recharge simultaneously from utility power, but they were damn fussy
> about generator power. Rather than fight them, we just did battery
> charging thru the SWs. We never had a utility outage longer than a day
> or so. So all I can say is that short term, they presented no problems.
> More battery capacity would have helped them greatly. The Best inverters
> certainly held up well. Ten years later we're still using the 3k unit. I
> suspect the efficiency really sucks, but efficiency is less of a concern
> with UPS units than rock-solid reliability.
>
> Doug Pratt
>
What will we do if there is another fuel shortage?
Did you know that there is a pollution free, completely
renewable fuel which you can use right now in your own car?
Don't replace the engine, replace the fuel.
Check out my website on making your own fuel:
http://running_on_alcohol.tripod.com
robertwarren at mail.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list