Xantrex versus Sunny Boy [RE-wrenches]
Kent Sheldon
kentsheldon at sbcglobal.net
Sun Aug 31 10:46:41 PDT 2003
Not entirely correct. 2% instantaneous loss is a bit low, but somewhere between 2-3% on a non-standard transformer is about right. Some transformers are much worse (5-6%) especially in the smaller sizes (10kVA). Now integrate the 2-3% instantaneous loss over the entire daily downtime of the inverter and compare to the PV power production throughout the day. The 2-3% becomes much larger compared to PV production. Have fun.
___________________________________
Kent Sheldon
Projects Manager, Industrial Power Systems
SMA America, Inc.
530 273 4895 ext 107
>>> Bill Brooks<billb at endecon.com> 7/31/2003 9:34:40 AM >>>
I don't think your efficiency numbers are correct. It is true the efficiency
is 96% BEFORE the transformer, but the transformer is going to consume an
additional 2%, not 6%. I still think you can put a 30kW inverter in a
smaller space than 12 SBs, but the difference may not be huge. The German
Mark is the other problem-cost.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list