Xantrex PV versus Sunny Boy [RE-wrenches]
max Balchowsky
max at seesolar.com
Wed Jul 30 20:30:47 PDT 2003
I've got 18 AEI inverters in the field. - 4 failures. 4 Xantrex in the field - 1 failure and 3 sub performers (compared to another manufacturer) and 1 Xantrex system failure due to faulty factory wiring and mis-information provided to field tecks over the phone while troubleshooting a system problem. 52 SMA inverters ( no failures and great performance ) - guess what I'm using exclusively now...........
I like the idea of using multiple 2500 watt inverters - redundancy adds protection against losing an entire system to inverter malfunction............A little more labor some would argue, but overall, I think it makes for a better, more reliable system........( we get 120 degree heat in the summer in Palm Sprimgs but most of out systems have inverters installed in a air-conditioned enviroment)....
Max Balchowsky
SEE Systems
100 S. Sunrise Wy #285
Palm Springs, Ca. 92262
Phone - 760-403-6810
Fax - 760-406-4230
"Building a Lasting Future For the Next Generation"
----- Original Message -----
From: <mlafferty at universalenergies.com>
To: <RE-wrenches at topica.com>
Sent: Wednesday, July 30, 2003 6:12 PM
Subject: RE: Xantrex PV versus Sunny Boy [RE-wrenches]
> Marco wants to know (paraphrased):
>
> What's better for a triple orientation, 30 kW PV System? 12 Sunnyboys
> or Xantrex PV Series?
>
> David B recommends (paraphrased):
>
> Go with the Sunny Boys. Mppt better, 1 failure not 100% failure,
> Isolation X-frmer losses 1-3% kWH AC, AC & DC Wiring smaller, faster,
> cheaper, etc.
>
> All:
>
> Great question for this list. My experience leans strongly toward
> David's point of view, especially when in higher ambient temps....Like
> Hawaii.
>
> The Mppt window of SB's vs. PV's strongly favors the SB. In addition,
> SB's posted efficiency #'s (CEC list) can be believed. PV's #'s don't
> include the iso transformers, based on the data I have. Of note is the
> fact that the SB's overall DCV-ACV headroom at 208 VAC is greater,
> yielding higher but undocumented (to my knowledge) kWH. First
> multi-system/multi-site 12 month Sacramento kWH/Capacity Factor data on
> 208 due in soon.... E-mail me OFFLIST at the end of August if you are
> interested in the data.
>
> Combining the triple orientation and related lower Vmpp associated with
> it will further enhance the SB's Mppt advantage over the PV for the
> described application.
>
> So far, the issues mentioned are more "Customer Satisfaction" related
> than "Contractor Related".... Read this as "Easier to meet Customer
> expectations with a clean conscience leads to reduced bad press and more
> sleep!" Or Surfing, as the case may be....
>
> Additional factors are the NEC / UL realities of Combiners and DC
> Fusing. By using Square D Discos, 12 SB's will only require 4, 1 per
> orientation, without a combiner (depending on the modules used). (Cost
> of larger DC Disco, Longer DC Runs, Combiner(s), Fusing, Wiring, Conduit
> & Labor is higher with the PV option.....Based on experience)
>
> Using a 120/208 Sub-Panel with breakers as individual AC Disconnects
> with a single larger AC Disco as the Utility Disconnect (If required -
> You should know that if anybody does...) is most likely a slight cost
> disadvantage to the SB. When you factor in the minimum two AC Discos
> required for the PV... One each side of the Iso X-frmer under Commercial
> NEC requirements... (often overlooked) and the associated Wire, Conduit
> & Labor, it's not as bad as it looks at first glance.
>
> Array equipment grounding should be a wash.... 30 kW @ 208 is 30 kW @
> 208, after all.
>
> Combine all the factors....Throw in a SB Control and you are sure to
> have a "Go Big Red" answer for this application.
>
> Pray for Sun!
>
> Matt Lafferty
> Universal Energies Institute
> mlafferty at universalenergies.com
> (916) 422-9772
> (916) 628-7694 Cell
> (916) 914-2247 Fax
> www.universalenergies.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list