You might have a hard time finding modules and
inverters that are listed for over 600vdc operation.
Seems like this would easily void any equipment
warranties.
Article 690-7(c) also says no pv source circuits over
600vdc in one and two family dwellings, or pv source
circuits over 600v that do not include lampholders,
fixtures, or recepticles.
Hope this helps,
Jerry Caldwell
--- Daryl Thayer <daryl_solar at yahoo.com> wrote:
> I have a similar problem with a SMA install where
> the
> open circuit voltage is above 600 just a little,
> maybe
> 700, and of course the peak power is well below 600.
>
> So I would like a PWM circuit that could limit this
> voltage to protect the SMA as I have heard of
> failures
> where the 600 volts is exceeded on open circuit.
>
> So does anyone know of a person that might design
> this
> circuit for me and how much would it cost?
>
> Daryl
>
__________________________________
Do you Yahoo!?
SBC Yahoo! DSL - Now only $29.95 per month!
http://sbc.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-wrenches
mailing list