cost per kWh [RE-wrenches]

Bill Brooks billb at endecon.com
Tue Jun 3 09:18:48 PDT 2003


Todd,

You are doomed to less the ideal performance. ;-)

Actually, the easiest way to see how bad of a problem it is--use a good AC
Watt meter to measure the output of the SW grid-connected with no critical
loads connected. Compare that value to the Volt-Amp output of the inverter
using a good true RMS clamp-on ammeter and a good voltage measurement. This
measurement should be done at or above 2kW of output.

One definition of Power factor is Watts/Volt-amps. If that value is less
than 0.8, you have a problem that should be fixed.

Bill.


-----Original Message-----
From: Todd Cory, Mt. Shasta Energy Services
[mailto:toddcory at finestplanet.com]
Sent: Monday, June 02, 2003 6:49 PM
To: RE-wrenches at topica.com
Subject: Re: cost per kWh [RE-wrenches]


Bill,

I remember that thread. My SW's software is too old (v3.0) to offer that
adjustment and as it is a series one unit (and I have the IC's) it is too
much
of a pain in the ass to swap chipsets since the unit needs to be taken off
the
wall to gain access.

Todd



Bill Brooks wrote:

> Todd,
>
> This is referring to the adjustment of PWM angle in the tech menus on old
> ETL listing SW inverters. There were several discussion a long time back
> about this and I can dig the info up off line if you like. I have heard it
> suggested that making this adjustment may change the anti-islanding
> characteristics of the unit. I have no data to confirm or deny it. I have
my
> doubts. If that was truly the anti-islanding method, I would want to have
a
> word with the designer on that one because it makes no sense.
>
> Bill.

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================








More information about the RE-wrenches mailing list