SW inverter to battery cable calculation [RE-wrenches]
Todd Cory, Mt. Shasta Energy Services
toddcory at finestplanet.com
Sat Nov 29 10:40:24 PST 2003
Are we talking about the DC load on the batteries when the inverter is supplying
AC power to loads, or the AC ripple on the DC fed to the batteries when the
inverter is grid connected and acting as a battery charger?
Todd
Bill Brooks wrote:
> John and Joel and Wrenches,
>
> The 28 amps comes from both John W. and myself. The actual calculation is
> found in my manual. The ripple current is very easy to read with a true RMS
> clamp-on meter. 28-amps is actually a conservative number and increases with
> increasing supply current. John B. does a nice job of explaining the issues
> below.
>
> Although there is no currently accepted method on how to deal with the
> issue, I put it in to get people thinking beyond the simple current flowing
> at lowest battery voltage. Ripple is a much bigger issue at 12 and 24 volts.
> My biggest question is not only what it does to the ampacity calcs on the
> conductors, but what does it do to the battery--it has to reduce battery
> life by increasing temperature at a minimum.
>
> Bill.
>
> -----Original Message-----
> From: John Berdner [mailto:jberdner at sma-america.com]
> Sent: Friday, November 28, 2003 12:02 PM
> To: RE-wrenches at topica.com
> Subject: Re: SW inverter to battery cable calculation [RE-wrenches]
>
> Wrenches:
>
> I "think" I know the answer Joel's question about where the extra 28
> Amps comes from.
> I would guess it comes from experimental data.
> I will ask J. Wiles and forward his reply.
> In the interim I will try to shed some light.
>
> I have discussed this issue many times with J. Wiles and the guys at UL
> and the rational is as follows:
> Normally we take the maximum ac output Watts / inverter efficiency at
> full power to get the maximum dc input Watts.
> Then we divide the maximum dc input Watts by the lowest battery voltage
> to get the maximum battery current.
> This current can theoretically be a continuous current so we need to
> multiply this number by 1.25 to get the NEC required ampacity for the
> battery cables.
> The problem with this approach is that it does not accurately reflect
> actual in field measurement of the current flowing in the battery
> cables.
> When you make RMS measurements of the current flowing in the battery
> cables you usually see a higher number than you would get from the
> straight dc calculation.
> The difference is due to the substantial 120 Hz ac ripple you see on
> top of the dc current when you measure the vast majority of inverter
> chargers.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list