  Well, the verdict is in. Sorry, it took me a day to get a KS cell so this 
six hour round trip didn't have to be repeated again.
  I took with me a 24 v, 100 watt bulb to act as a load since I didn't want 
the inverter to go into involuntary shutdown any more. After taking SG 
readings on each cell (1.27 + for each one) and voltage readings(again) on 
each one (2.13 - 2.15) I divided the bank into 2 24 volt banks and put my 
load (the bulb) on the first one.It ran fine and I checked each 2 volt cell 
and got almost the same exact reading as I did without the load. OK, that 
half of the bank is good.....
  I next did the same with the second bank. The bulb lit up and immediately 
dimmed. The fourth battery in the string, which read 2.13 v no load read
 -.78 v. The polarity was reversed internally.
  I replaced the cell, retested the bank (the bulb didn't dim) and took 
readings on the rest of the cells. They were all fine.
  After tightening all connections I fired up the system and ran some larger 
loads (refrig. well pump) and all was/is well.
  After this experience this NABCEP test this weekend is looming extremely 
large in front of me...............
  Thanks for all who contributed.
Daryl
Penobscot Solar Design 

 

Carl Emerson, Free Power Ltd. writes: 

> Hi gang, 
> 
> I have struck one bad cell going into reverse polarity and pulling the 
> bank voltage down big time.. 
> 
> We will soon all know I guess. 
> 
> Cheers 
> 
> Carl Emerson
> Free Power Ltd.
> Auckland NZ 
> 
> Jay Peltz, Peltz Power wrote: 
> 
>> HI all, 
>> 
>> 
>> I think that its time to get the clamp on amp meter here.  You should be
>> able to pinpoint the  bad connection via that.  I do agree that the 
>> problem
>> is a bad connection ( battery cable) or a bad cell..  Also you should be
>> able to increase the load and measure the voltage drop and find the 
>> problem. 
>> 
>> Please keep us informed as to what it turns out to be!! 
>> 
>> 
>> jay 
>> 
>> Peltz PowerJay Peltz, Peltz Power wrote: 
>> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com 
> 
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/ 
> 
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm 
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html 
> 
> Hosted by Home Power magazine 
> 
> Moderator: michael.welch at homepower.com
> 
>  
> 
 

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------


</x-flowed>



More information about the RE-wrenches mailing list