Ray Walters said:
***
NO one has mentioned in this thread that the SW5548 is terrible at
surges.
I've been disappointed that it trips its over current switch when a
lowly
DR2424 can hang in there.
***
It's true the SW5548 doesn't surge as well as the 4kVA SW units. I
believe it's been discussed in the past on this list. The reason I was
given is that the 5.5 kVA unit was intended for more sensitive loads and
doesn't allow the voltage to sag as much as the smaller units when
starting large motor loads. Thus better power quality means less surge
ability.
Eric Smiley, BEng, MASc
Project Leader
Photovoltaic Energy Applied Research, Technology Centre
British Columbia Institute of Technology
NE25 - 3700 Willingdon Avenue
Burnaby, British Columbia
Canada V5G 3H2
phone: 604.432.8657 fax: 604.436.0286
esmiley at bcit.ca www.tc.bcit.ca
The information contained in this E-mail is intended for the addressee
only. If you have received this in error please delete it.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list