T-240 circuit problem [RE-wrenches]
Matt Tritt
solarone at charter.net
Tue Sep 2 19:10:10 PDT 2003
Ray,
Thanks for the words of caution. However - I am going to make the
assumption that you live somewhere East of California, Oregon and
Washington. In California (where lawyers are hiding behind every water
tank) and most of the West, it's not only legal to store potable water
in an above-ground tank, it's the accepted norm. The exception is if you
are pulling water from a surface source such as a spring or creek. Then
the health department requires a test for bacterium and viruses. This is
a non-specific test by the way. If it comes back positive you have to
take steps to clean up the water before it comes into the house. I
usually use ultra-filtration, ozone and RO in those cases. No one has
gotten sick using water from my systems yet; if they have, they ain't
talkin! (and I've been putting them in for about 30 years)
Most of our wells are 150' to 500' deep with water generally standing
around 80+. All wells are sealed against surface contamination and all
require a well report be submitted to the County. I always decontaminate
tanks and plumbing when starting-up a new system with Calcium
hypochlorite or Hydrogen peroxide. Safety First!!!!!!!!!!!!!!!!!! :-)
Once the system is in and working, the chances of a tank becoming
contaminated are virtually nil (unless someone mistakes the manhole for
a toilet).
Matt T
-----Original Message-----
From: Ray Walters [mailto:remotech at taosnm.com]
Sent: Tuesday, September 02, 2003 10:32 AM
To: RE-wrenches at topica.com
Subject: Re: T-240 circuit problem [RE-wrenches]
Hi All;
Ample water storage is a good idea; pumping it into the house and
thinking
its potable is NOT. I would recommend a sealed system for water supply
to
the house and a cistern (rain catch possibly) with a pressure pump to a
yard hydrant for fire protection and gardening. I've seen most cistern
systems fail water quality tests due to coliform type bacteria. Unless
you
want to start chlorinating the cistern regularly, I'd look at the sealed
system only.
Not to be a lawyer, but the liability of customers contracting Giardia
isn't worth it.
Ray Walters
Taos Power, SolarRay
At 04:06 PM 8/30/2003 -0700, you wrote:
>Bob-O et al,
>
>It's good to know that the SQ will work with inverters. Maybe I need to
>change my AC pump supplier. I don't see the reason to run a
>pressurizing sub pump - sans water tank though. If you live outside the
>distributed water supply, you'd have to be slightly out of yer gourd
>NOT to have a nice, big holding tank, a 4" supply to (at least) one
>hydrant, and a booster pump for other purposes, unless there's a good
>fall from the tank. This is like running an off-grid house with four
>T-105's and hoping that the power input never goes off!
>
>Matt T
>
> Message -----
>From: "Bob-O Schultze, Electron Connection" <econnect at snowcrest.net>
>To: <RE-wrenches at topica.com>
>Sent: Saturday, August 30, 2003 3:07 PM
>Subject: Re: T-240 circuit problem [RE-wrenches]
>
>
> > Matt, Dave, etal,
> > I've got a few SQE pumps running on sine wave inverters with no
> > worries both in 120V (now discontinued, I think) and 240V through a
> > T240. I did, however, have one bummer SQE which worked out of the
> > box but poorly. More poorly on the inverter than the genny. Dontcha
> > hate that? Grundfos gave my supplier credit for it eventually, but
> > it was a hassle with me having to buy a second pump to get the
> > client back in water. I was very unimpressed by the glacial speed at
> > which Grundfos dealt with the problem. Best, Bob-O
> >
> > >Dave,
> > >
> > >As I remember, the SQ is a variable speed, constant pressure pump,
> > >which includes an inverter within the pump itself. They might be
> > >trying to run
>an
> > >inverter with another inverter - a function which is highly
> > >improbable,
>if
> > >not impossible. (This according to Hays Pump who also make a
> > >similar type
>of
> > >pump I was interested in powering with a 4048 a few years ago)
> > >
> > >This pump will run great on generator power or grid, but not on
> > >inverter power.
> > >
> > >Matt T
> > >
> > >
> > >----- Original Message -----
> > >From: "David Palumbo, Independent Power & Light" <ipl at sover.net>
> > >To: "Wrenches" <RE-wrenches at topica.com>
> > >Sent: Saturday, August 30, 2003 8:54 AM
> > >Subject: T-240 circuit problem [RE-wrenches]
> > >
> > >
> > >> A customer reports the following:
> > >>
> > >> 240v water pump operating off of OutBack FX2024 inverter by way
> > >> of a
>Trace
> > >> T-240 (we specked Trace because T-240 comes with box and
> > >> customer did
>not
> > >> have OutBack AC box on his system) making loud "grinding noises"
> > >> while attempting to power the water pump. The pump is a Grundfos
> > >> SQ sub pump pumping into a standard pressure tank setup. FX
> > >> inverter appears to be operating fine as he reports no problems
> > >> with other loads.
> > >>
> > >> TriMetric system monitor showed current going from normal 45
> > >> amps dc
>at
> > >24v
> > >> up to 90 amps during this episode. He reported that these
> > >> numbers were jumping back and forth violently and the TriMetric
> > >> meter actually
>re-set
> > >> itself to 100% at this time.
> > >>
> > >> I told him to check all his connections etc. He said he had
> > >> already
>done
> > >> that. I had him then disconnect the pump feed wire from the
> > >> T-240 and connect the pump directly to his 240v generator
> > >> output. He called back
> > >later
> > >> to report that he tried this and the water pump worked fine
> > >> directly
>from
> > >> the generator.
> > >>
> > >> He has had the T-240 working in his system since early spring
> > >> with
>good
> > >> performance until now.
> > >> The circuit is as follows: FX2024 > 120vac load ctr > 15A
> > >> breaker >
> > >pressure
> > >> switch > T-240 T-former > 240v Grundfos SQ sub pump.
> > >>
> > >> Do Transformers go bad? Or what else might cause this problem?
> > >>
> > >> Thanks,
> > > > Dave
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages:
> > http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette:
> > http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
> >
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list