Scott;

I agree with Matt. Actually, I've found that most problem loads for Mod 
sine inverters don't do much better on SW's stepped wave. I spec SW series 
inverters for the generator start or other special features, but I spec the 
Exeltech or Outback for tricky control stuff. I've been burned too many 
times by Xantrex's claims of compatibility. Xantrex has a list of all the 
problem loads but they don't publish it. Don't use an SW for:
Sound or recording equipment
Variable speed motors with electronic controls
Household automation stuff
I often use a good old DR series for most of the house and have an Exeltech 
feed a couple of special circuits. This offers cleaner power for the loads 
that need it, more surge for starting  big stuff (a DR3624 will outsurge an 
SW4048 every time), offers redundancy, and still comes out cheaper than an 
SW4048.
A  bandaid that got us by a few times is to put a 50microF cap across the 
SW inverter's AC output.

Ray

Solarray.com, AKA Remote Technology, AKA Taos Power


>Scott,
>
>The simple remedy is to replace the SW with an Outback! The SW has too few
>steps in it's "sinewave" to fool some electronics and some fan motors. The
>SW also, in spite of advertising claims to the contrary, produces an audible
>60 cycle buzz on many different types of telephone equipment. Perhaps the
>guys at Outback could try one of these fans on the 2000?
>
>Matt T
>----- Original Message -----
>From: "Scott: Backwoods Solar" <scott at backwoodssolar.com>
>To: <RE-wrenches at topica.com>
>Sent: Thursday, June 12, 2003 8:21 AM
>Subject: Remote Control Ceing Fan [RE-wrenches]
>
>
> >
> > Good Morning Wrenches,
> >
> > We have a customer who has a new Casablanca remote control only ceiling
>fan.
> > They have a SW4024 inverter which won't operate it. They tested the fan at
>a
> > home with utility power and it worked. They also tested it with a Honda
>3500
> > watt generator which is wired into their SW4024. Once the "AC2 in" was
>good,
> > the fan worked. Turn off the generator; inverting resumes; and control of
> > the fan was lost although it did continue to rotate but at fewer rpms and
> > with a hum not present on grid or generator power.
> >
> > Have other's had this SW problem with remote controlled fans? Are there
>any
> > remote controlled ceiling fan models which are known to work with the SW
> > series? Any solutions to the present problem which might allow the current
> > fan to operate?
> >
> > Thanks.
> >
> > Scott
> >
> >

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================



</x-flowed>



More information about the RE-wrenches mailing list