ground resistance [RE-wrenches]
Bill Brooks
billb at endecon.com
Wed Apr 23 12:42:10 PDT 2003
Jay,
Grounding system tests are not often done in the field (frame to ground
resistance). The only way a reading has any validity is if the resistance
measurement is made at full ground current. Continuity or resistance checks
at zero current is almost meaningless. As soon as current flows, resistance
of all connections change--particularly simple metal-to-annodized aluminum
contact.
Bill.
-----Original Message-----
From: Jay Peltz, Peltz Power [mailto:jay at asis.com]
Sent: Wednesday, April 23, 2003 8:11 AM
To: RE-wrenches at topica.com
Subject: ground resistance [RE-wrenches]
HI Bill and John,
In checking exsisting systems for ground bonding to mounting frames, what
readings should I be looking for. IE whats too high?
Thanks,
jay
Peltz Power
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-wrenches
mailing list