Another reason to dislike tray cable [RE-wrenches]
Bill Brooks
billb at endecon.com
Mon Apr 21 15:05:15 PDT 2003
William,
Are you referring to two-conductor tray cable or USE-2 cable?
I don't know that you are violating the listing if you cut the MC connector
off as long as you use UL-listed parts to connect into a properly rated and
sized junction box. By the way, refer to THHN as THWN--a minor point, but
THHN is only allowed indoors.
Just to smack the hornet's nest--flexible non-metallic conduit still doesn't
have the proper ratings to connect directly to a junction box on a PV
module.
Bill.
-----Original Message-----
From: William Miller [mailto:wrmiller at slonet.org]
Sent: Monday, April 21, 2003 2:22 PM
To: RE-wrenches at topica.com
Subject: Another reason to dislike tray cable [RE-wrenches]
Friends:
I am bidding an off-gird installation. The customer purchased his
equipment from a well known mail order outfit. He has mounted his 8 Sharp
165 modules on two fixed, pole mount racks. I need to connect the Sharp
modules to the Outback PV combiner. Each module is a separate feed to the
combiner, since the system is 24 volt, nominal. I can't just run the tray
cables to the combiner because 1, they aren't long enough and 2, there is
no hardware I know of to bring the tray cables into an enclosure. The tray
cables with MC connectors are meant to connect to another MC connector. If
I cut the MC connector off to feed the lead into a J-box, I void the
warranty of the module.
Here's the only way I can see to connect these modules up: I provide a
J-box on each pole with 8 tray leads hanging out of the bottom, each with
an MC connector. To do this, I need to spend $192.80 and lots of time.
Below is an "ÄSCII" CAD drawing, if it doesn't get hacked up by line
wrapping:
-------------------------------------
Module plus -----> >----Gland nut-| box ---splice-------THHN--|----\
Module plus -----> >----Gland nut-| box ---splice-------THHN--|----\
conduit-----combiner
Module neg -----> >----Gland nut-| box ---splice-------THHN--|----/
Module neg -----> >----Gland nut-| box ---splice-------THHN--|----/
-------------------------------------
For each mounting pole I need to provide a J-box. In each J-box I need to
bring in 9 leads (4 modules with plus and minus and a ground). I need 8
gland nuts (Arlington LPCG50, $1.10 each) on the bottom of each J box. I
can't use a standard metallic Nema 3R box because by the time I find one
with 8 existing KOs or room to add enough KOs to total 8, it would be huge.
So I need an 8X8X4 plastic J box (Carlon E898N, $24.00). Then I need to
purchase 8 prefabricated tray cables with MC connectors ($14.00 each). I
cut each one in two and install one end in each gland nut. Once in the
J-box, I need to get my leads over to the combiner. I run PVC conduit from
each J-box to the combiner. If I put the combiner on one of the two poles,
the tray leads from the J-box on that pole might be long enough to reach
the combiner, but the leads from the other pole are not. I need to splice
the tray leads (the ones in the gland nuts) to some THHN. I could use wire
nuts, but I prefer a terminal strip ($24.00).
***snip***
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-wrenches
mailing list