600 VDC switches [RE-wrenches]
Brad Bassett
bsbassett at earthlink.net
Thu Feb 13 12:34:16 PST 2003
Bill, the Isc is 5.46A, so 5.46 x 2 x 1.25 = 13.65A
4.77A is the Imp. I think designing to Imp might be more realistic
though. Or take the PV 1.25 off the Isc. I've never seen Isc x 1.25
continuously (3 hours).
Brad
Bill Brooks wrote:
> Brad,
>
> I'm not sure that this question got answered. John Berdner probably
> knows
> better than I, but my understanding is that 13A is a continuous rating.
> The
> issue with a disconnect is what happens when it opens anyway, so it is a
> bit
> different than wire. However--the proper way to size is based on 690.8
> which
> says you take the total Isc of parallel strings and multiply by 1.25.
> The
> Isc of the 165-Watt module is 4.77 amps so max current is 12 amps (4.77A
> x 2
> x 1.25 = 11.925).
>
> Some bright guy must have picked that 13 amp number.
>
> Bill.
>
>
> -----Original Message-----
> From: Brad Bassett [mailto:bsbassett at earthlink.net]
> Sent: Wednesday, February 12, 2003 9:18 AM
> To: RE-wrenches at topica.com
> Subject: SPAM: RE: 600 VDC switches [RE-wrenches]
>
>
> John,
>
> I have not seen an answer to this question. If you feed an SB with two
> strings of modules, the 13A limit is likely to be exceeded if it is not
> rated for continuous. With the 165's it's exceeded even at PV 125%.
>
> Thanks,
> Brad
>
>
> William Miller wrote:
> > The rating is for 13 amps per pole. Is this de rated for continuous, or
> > for PV?
> >
> > Thanks again,
> >
> > William
> >
> >
>
>
>
>
> Brad Bassett
> Schott Applied Power
> Tumwater, WA office
> bsbassett at earthlink.net
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
>
Brad Bassett
Schott Applied Power
Tumwater, WA office
bsbassett at earthlink.net
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-wrenches
mailing list