One real issue to watch out for on the ProSine 2.0 is that the transfer
switch is only 30 amps and the charger is completely backed off at 24
amps of pass thru AC loads (80% of the max input breaker rating I
guess).Then the inverter not only does not charge but it actually starts
consuming 5 amps DC from the battery. The battery voltage drops even
though the generator is running.