Caveat of battery bank on Grid tied SW inverter [RE-wrenches]
Dan Duffield
dand at directpower.com
Fri Aug 8 13:01:26 PDT 2003
<x-flowed>
What's the smallest 24 or 48 V battery bank out there on a grid-tie SW
inverter?
About five years ago our company was contracted for a PV
installation (only) on a National Historic Site in New Mexico, (so the
system design was out of our hands), but the prime contractor selected a
SW5548 for this grid-tie application and only 4 - group 27 batteries were
spec'd in approx (96 A-Hrs @ 48vdc). The array was 1530 watts, we should be
able to sell 10, 11 or 12 amps of 120VAC power.
Two interesting notes
What happens if the grid goes down when all of or something close
to 5500 watts are being pulled from this size inverter during a power
outage, - loads will be of be transferred to the battery bank, let see
5000/48 = 104 + amps, that not a safe C/3 rate for this many
batteries: that's more like a C/.92 rate - battery meltdown - however,
the voltage may drop soon enough to turn inverter off when pulling this
high a wattage from our battery bank, but what if were pulling some where
in between, say at C/1.5 rate or around 2300 watts - the voltage will stay
up long enough to let the battery get real warm, their exists no way to
easily "be confident" that this is not a safety issue, so I put an
appropriately smaller Heinemann breaker to prevent this from occurring.
As a result of this, we installed the mentioned circuit breaker
sized to allow a C/3 rate but no more - if utility power failed; to let
2300 watts pass out of the protected battery. So a 35 amp Heinemann was
installed. Everything OK ? Nope. When the grid was "up", and the site was
selling/buying, this breaker was experiencing nuisance trips.
We checked the float voltage, We were not selling battery
power We checked Maximum Sell Amps AC which was well below the DC
side circuit breaker rating, but it did'nt seem to be working - were we
selling battery power - it was tripping - why?.
It turns out- that the SW5548 was trying to help or smooth out the
voltage drop spikes using the battery bus voltage. Way out at the end of
the rural community where this system was located -the grid voltage
regulation was a little "loose", from other customer's in the area and
their inductive loads like well pumps and compressors. We swapped out the
35 amp Heinemann for a 40 amp circuit breaker, still had these nuisance trips.
We had turn lower the Maximum Sell Amps AC setting, to reduce
pulling high instantaneous amp values from the battery bank to do this
local voltage regulation. "Maximum Sell Amps AC" on the SW series - this
control is relatively slow. Where we shoulda, coulda, woulda sold at 10 or
11 amps, we had to bring max sell amp value down to 8 amps - to prevent
this nusiance tripping. It was our only solution, On future applications
this could affect the sizing of a PV arrays- why have the extra PV wattage
if you cant sell it? i.e., (Maximum Sell Amps AC) and time of day usage.
--
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list