Using transformers at other voltages and Frequencies [RE-wrenches]
Daryl Thayer
daryl_solar at yahoo.com
Fri Aug 1 07:38:00 PDT 2003
Thanks to everyone
For all the help with using a transformer at other
frequencies.
It appears it will work, at increased losses, and at
one half the power at 30 cycles, by using 1/2 the
voltage. My application is I was hoping to use the
upper end of the power curve of the wild AC from a
wind machine. HOwever I will need larger
transformers. The Outback is rated at 4kW at 60
cycles, and then would be only 2kW at 30 Hz.
Thanks DAryl
--- Hugh Piggott <yahoo at scoraigwind.co.uk> wrote:
> At 4:32 PM +0000 29/7/03, aerofirewp wrote:
> >Daryl
> >
> > I would disagree with Jim about 30 hz being a
> problem ,
> >because of the fact that you are also halving the
> input voltage.As
> >long as the volts/hz is the same or less you will
> not saturate the
> >core and draw excessive magnitizing current.
>
> I agree. Halve the voltage and halve the frequency
> at the same time.
> I do this quite often. The transformer will work
> fine but it is true
> that you can only put 1/4 the power through it at
> that voltage if you
> want to keep the same % efficiency (the same % of
> the power lost in
> the copper resistance).
>
> Buy a bigger transformer if you need one. No need
> for a special one,
> so long as you watch the volts.
> --
> Hugh
>
> http://www.scoraigwind.co.uk/
>
__________________________________
Do you Yahoo!?
Yahoo! SiteBuilder - Free, easy-to-use web site design software
http://sitebuilder.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list