grounding plate vs. rod? [RE-wrenches]
David Blecker
blecker at seventhgenergy.org
Wed Dec 18 07:21:33 PST 2002
<x-flowed>
Scott,
A one inch dia, 8 ft long ground rod would provide almost as much surface
area as the plate IF you can drive a rod in and IF the soil conductivity is
high enough to create a solid bond. Have you verified the soil type or is
the plate approach just how things are done? My experience working with
Native tribes is that the white guy's mind-set to "get it done quick"
should usually defer to local knowledge and custom for whatever its worth.
Good luck and send tea!
David
At 01:12 AM 12/18/2002, you wrote:
>Hello, all.
>
>I'm installing PV in Nepal for a Kathmandu-based company. They typically use
>copper grounding plates (18"x18") here rather than the grounding rods I'm
>familiar with back in the good ol' USA. Our Nepali techs claim that the
>local soil composition necessitates taking extra steps to increase its
>conductivity. That is, using the larger surface area of a plate as opposed
>to a rod and burying it parallel to the surface, two or more meters deep
>sandwiched between two layers each of salt and coal. Does this sound
>reasonable/plausible? As you might imagine, driving a grounding rod is much
>more appealing to me than (hand) digging a 24-inch diameter hole, 7+ feet
>deep.
>
>Thanks in advance for you insights.
>
>Scott Russell
>Lotus Energy, Kathmandu
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
----------------------------------------------------------
David Blecker, P.E., Director
Seventh Generation Energy Systems
608-424-1870 (ph) 424-1810 (fax)
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list