DC-GFP/2 protection [RE-wrenches]
Joel Davidson
joeldavidson at earthlink.net
Fri Aug 23 08:48:41 PDT 2002
All good points, but it is not expensive and is worth the time to measure
resistance (<5 ohms) between equipment and the earth.
Ray Walters wrote:
> Hi Guys;
>
> Well I fried a pair of SW4048s and we DID ground negative. Jeff, when you
> say that the PV frame and AC were properly grounded, what testing did you
> do to determine that? What was the resistance or (more importantly for
> lightning protection) what was the impedance to ground? What are the soil
> conditions at the site? To say it was properly grounded, you really need to
> answer those questions or you need to tie to a steel cased well. When the
> ground is questionable, I now advocate floating DC negative.
>
> Here's the choices:
>
> 1.Expensive ground testing and certification.
> 2 Bond to a steel well casing.
> 3.Sink two rods and consider floating the DC negative and adding extra
> protection.
>
> Even if you do everything by the book or beyond, you may someday have an
> installation damaged. Check out Polypasher, they protect communications
> towers that take so many direct hits,they install "Event" counters. I'm not
> hawking their wares, (that previously mentioned system had some of their
> stuff and Delta LAs) but they really have studied this stuff in depth.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list