Inverter Testing--Continuing the thread [RE-wrenches]

Bill Brooks billbrooks7 at earthlink.net
Thu Apr 18 15:30:34 PDT 2002


Peter,

You have put your finger on an extremely common misconception. Most think
that PTC conditions on the CEC website were actually tested by someone other
than the manufacturer. Not so--the PTC module ratings are based solely on
manufacturer's information of STC and NOTC and those data are used to
calculate what the PTC would be. Nearly all manufacturers are on the low end
of +/- tolerance spectrum, so this number on the CEC website is almost
always 5-10% higher than what the rating would be from an independent lab.

Since you touched on the inverter efficiency ratings (as is this thread is
addressing), those numbers are strictly based on information from the
manufacturer. Sometimes we ask "is that your final answer" when we think the
number sounds unusually high, but if the answer comes back "that's my final
answer" then Regis hands out the $1,000,000 (actually Jeff Newmiller updates
the website). It is certainly possible that one manufacter is very
conservative with their numbers and others have a "rounding up" tendency.
There is no standard to prevent that. Have I depressed you yet?

Peak efficiency is a number to maximize the buydown and should never be used
to determine how much power or energy a PV system will produce. Ultimately
it is all about how much energy a PV system generates on a annual basis.
ACout divided by PVin on an annual basis is a much better metric than max
efficiency. 90% efficiency is a very high number and some inverters come in
at 80-85%.

Efficiency can be affected by temperature, voltage, and certainly power
level. As a manufacturer, you pick the right conditions that maximize the
number, round to the nearest higher digit and go with it--a little tongue in
check for fun but not too far from the truth. Without anyone telling them
how it must be done, I can't say that I blaim them--it just doesn't help the
wrench or the customer with anything other than a higher rebate.

Bill.


-----Original Message-----
From: asap at podnine.com [mailto:asap at podnine.com]
Sent: Thursday, April 18, 2002 2:50 PM
To: RE-wrenches at topica.com
Subject: RE: Inverter Testing--Continuing the thread [RE-wrenches]


Wrenches,

Does not the CEC's PVUSA test conditions, the infamous PTC ratings, kind of
tell the story and level the playing field with their eligible inverter
ratings?  Hasn't this been done before?

http://www.consumerenergycenter.org/buydown/certified_inverters.html

Anyone know how these ratings happen, how testing is done or what "based on
available documents" means, and who gets to decide on these peak efficiency
ratings?

Peter Duchon
ASAP POWER!

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================








More information about the RE-wrenches mailing list