Lightning Revisited [RE-wrenches]
Drake Chamberlin
solar at eagle-access.net
Tue Apr 16 17:18:35 PDT 2002
<x-flowed>
At 11:09 AM 4/16/02 -0700, you wrote:
>Drake -
>
>Inductance works not by raising the potential of each of the conductors
>a set amount all along the conductor. Inductance causes an
>electromotive force AROUND a circuit which is proportional to the time
>rate of change of the magnetic flux through the circuit. The "magnetic
>flux through the circuit" is the amount of magnetic field through the
>area of the circuit.
That is why I used the example of 2 wires in a conduit. Both conductors
would be exposed to approximately the same flux. The magnetic field would
cut through the conductors equally, as they would be in very close
proximity. All along their length they would be getting equal exposure as
the magnetic pulse rose and fell.
Code, in general, requires wires of the same circuit to be run
together. Both wires would rise in voltage at the same rate. Voltage is
relative. Ground potential is arbitrary.
> That is why the problems with a large series
>circuit in which the wire returning current from the extreme panel does
>not return along the same path as the wires connecting the panels.
That would definitely be a problem.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list