> I asked around our office and the consensus was to tie all of the grounds
>together, if possible, to reduce the potential for current flow in the
>grounded conductor from structure to structure.
It is important not to parallel both neutral wires and equipment grounds
from structure to structure, as it will provide parallel neutral current
paths. Separate ground rods are not considered a ground path. A metal
conduit bonded to equipment in both structures is.
-Drake
- - - -